Charging on Dryer Outlet

LinkRS

Well-Known Member
First Name
Rich
Joined
Sep 2, 2022
Threads
11
Messages
146
Reaction score
135
Location
Texas
Vehicles
2023 Mustang Mach E GT Performance Edition
Occupation
Software Engineer
Country flag
The advice posted does *NOT* contradict what's on the website, in my opinion. The website is just a little.... amibiguous? Or .... wrong?

"Plug into any 240V", the website says. Not true --- plug into any 240V you*can* plug into. The Ford charger supports only NEMA 14-50. A 14-50 has to be fused to 50A (and would be better installed as 60A because it could be a continuous load but in either case the 42A charger is safe).

If you get an adapter to a 30A plug, put their 42A charger on a 30A circuit... You'll have a bad time. The breaker should blow. You shouldn't get a fire, because that's what breakers do, but if your breaker malfunctions, then you probably will get some very bad juju (melted wires and shit smoking if not catching fire). As they say, "not recommended". In any case, it won't / shouldn't work - it should trip breakers.

If you're going to use adapters, you really need to know what you're up to. All these plug formats exist for a reason, and an adapter circumvents the physical safety mechanism, which requires you to use the safety mechanism called your brain --- something designers consider a terrible, terrible idea.

You almost certainly need a charger that supports setting the Amperage. I've been looking for one, myself, because if my mobile charger is my "last resort", then I want to be able to set it to a number of values.... Who knows if I'm at my friend's house and they say "wellll..... I know it's a 50A plug but my shady cousin put in low grade wiring...."

But I haven't found a charger that goes all the way from 16A to 42A and is portable enough to replace the Ford unit in the space under the floor in the car.

Looking for recommendations; I haven't searched the last 6 months.

[ I might even say 50A is not unreasonable.... But the cases where 50A are safe is super rare.... SUPER RARE.... 42A would be fine with me ]
Thanks @bbulkow! I appreciate you taking the time to respond. So I take this to mean that a nema 14-50 expects a 50 amp circuit, and why it didn’t fit my dryer plug. So glad I didn’t try it, I just used 110 until I had my 48 amp L2 evse hard-wired to a 60 amp circuit.
Sponsored

 

ocdxfv

Well-Known Member
First Name
Matt
Joined
Feb 11, 2021
Threads
19
Messages
250
Reaction score
329
Location
Orange County, CA
Vehicles
2021 Mach E, 2013 Toyota Rav4 EV
Occupation
Retired radiology tech
Country flag
I’ve been successfully charging on a dryer outlet since I bought my first EV in 2013. I charge pretty much every night and I don’t recall ever waking up to a car that was not fully charged. All that’s needed is an EVSE that can be set to 24 amps max continuous (not the Ford unit). Currently I’m very pleased with my hard wired Tesla Wall Connector.
Ford Mustang Mach-E Charging on Dryer Outlet IMG_3502
 

65MustangBoy

Well-Known Member
First Name
Les
Joined
Jan 27, 2023
Threads
8
Messages
197
Reaction score
239
Location
Indiana
Vehicles
65 Mustang, 2023 Mach E Premium
Occupation
Retired
Country flag
Thanks @bbulkow! I appreciate you taking the time to respond. So I take this to mean that a nema 14-50 expects a 50 amp circuit, and why it didn’t fit my dryer plug. So glad I didn’t try it, I just used 110 until I had my 48 amp L2 evse hard-wired to a 60 amp circuit.

I'm an EE and don't usually jump into these topics. However, the answer to your question is sort of... yes. A NEMA 14-50 is RATED up to 50 amps at 240V. So you also need 50-amp capable wiring from the outlet to the 50-amp circuit breaker in your panel. I hope that makes sense. You should NOT connect a NEMA 14-50 to wiring that is only capable of handling 30 amps. And you certainly CANNOT just swap out a 30-amp breaker with a 50-amp breaker and leave your 30-amp cabling in-between. The wire will get HOT. To be clear the scenario I just described is a NEMA 14-50 with 30 amp wiring to a 50-amp breaker. (BIG NO-NO).

This is why there are different configurations of 240V outlets and plugs. Just because they are 240V capable, you CANNOT ignore the amp carrying capability all the way from the breaker panel, the breaker, the wiring, and the outlet. One of the primary benefits of 240 circuitry is the additional amp carrying capability it has.

My last point is the topic of "continuous use." To avoid a possible fire in the future I always design for worse case. That means I assume "continuous use" whether I use it continuously or not. For continuous use you want to only run at 80% of what the circuit is actually capable of. That being said... That means if you run a 60amp breaker, 60 amp carrying wiring, to a 60 amp termination. I used the word termination as this is the way many "hard wired" ESVE's are used. There is no outlet/plug. They are hardwired in. So for a 60 amp, hardwired ESVE I still would only ever run it at 48 amps (80% * 60 amps).

For your 50 amp NEMA 14-50 outlet/plug combination I would still limit the EVSE to 40 amps (80% x 50amps).

I hope this helps.
 

21st Century Pony

Well-Known Member
First Name
Martin
Joined
May 21, 2022
Threads
36
Messages
1,976
Reaction score
2,243
Location
Arlington, Virginia
Vehicles
formerly Ford Mustang Mach E 2022 Premium AWD ER, now a li'l bit of Lightning ER
Country flag
I'm an EE and don't usually jump into these topics. However, the answer to your question is sort of... yes. A NEMA 14-50 is RATED up to 50 amps at 240V. So you also need 50-amp capable wiring from the outlet to the 50-amp circuit breaker in your panel. I hope that makes sense. You should NOT connect a NEMA 14-50 to wiring that is only capable of handling 30 amps. And you certainly CANNOT just swap out a 30-amp breaker with a 50-amp breaker and leave your 30-amp cabling in-between. The wire will get HOT. To be clear the scenario I just described is a NEMA 14-50 with 30 amp wiring to a 50-amp breaker. (BIG NO-NO).

This is why there are different configurations of 240V outlets and plugs. Just because they are 240V capable, you CANNOT ignore the amp carrying capability all the way from the breaker panel, the breaker, the wiring, and the outlet. One of the primary benefits of 240 circuitry is the additional amp carrying capability it has.

My last point is the topic of "continuous use." To avoid a possible fire in the future I always design for worse case. That means I assume "continuous use" whether I use it continuously or not. For continuous use you want to only run at 80% of what the circuit is actually capable of. That being said... That means if you run a 60amp breaker, 60 amp carrying wiring, to a 60 amp termination. I used the word termination as this is the way many "hard wired" ESVE's are used. There is no outlet/plug. They are hardwired in. So for a 60 amp, hardwired ESVE I still would only ever run it at 48 amps (80% * 60 amps).

For your 50 amp NEMA 14-50 outlet/plug combination I would still limit the EVSE to 40 amps (80% x 50amps).

I hope this helps.
^^ This^^ is a thorough reply and great advice.
 

WR221

Well-Known Member
First Name
Bill
Joined
Feb 15, 2024
Threads
0
Messages
54
Reaction score
37
Location
Maryland
Vehicles
2021 MME CR1, 2022 KIA EV6
Occupation
Retired Physicist
Country flag
My Grizzl-E charger has dip switches inside the unit to reduce the power from 40A to 32A, 24A or 16A. You could set it low and it would not be possible to go higher by mistake.
 


MillerPaints

Active Member
First Name
Wendy
Joined
Mar 9, 2023
Threads
1
Messages
28
Reaction score
21
Location
California
Vehicles
2023 Mach E Premium RWD SB
Country flag
I use a Dryer outlet to charge but I got a SplitVolt switch and a SplitVolt charger for 10-30 which is the type of dryer outlet I have. You cannot use a 14-50 charger on a 10-30 or 14-30 outlet since those are 30 amp max and the 14-50 is a 50 amp outlet but requires the correct wire cable to the outlet to withstand the higher current level. The Ford charger cannot be dropped to the lower current. My SplitVolt charger draws just under 24 amps which is about the most you would want on a 30 amp circuit at continuous use. The SplitVolt switch will switch between the dryer and the charger when the dryer is started. I have not done it since I make sure not to use the dryer when the car is plugged in. Otherwise the dryer seems to work like it always has.
WE do the same thing....my husband did a lot of research before we bought the car. We have a ranch style house and our electrical panel is on one end and the garage on the other so it was going to be ridiculously expensive to run another 220 line. We did have an electrician come out to inspect our dryer plug and make sure it had the proper grounding, etc. We purchased the Split Volt switch and charger and have not had any issues. :)

Ford Mustang Mach-E Charging on Dryer Outlet PXL_20230225_232041709
 

Fins160

Well-Known Member
First Name
JP
Joined
Apr 7, 2022
Threads
11
Messages
235
Reaction score
270
Location
Tempe, AZ
Vehicles
2022 MachE Select C/T Dark Matter Gray
Occupation
Engineer
Country flag
A second (or third or fourth) recommendation for the Splitvolt system. It's specifically designed for your scenario, and includes a local circuit breaker for an additional level of safety. In my experience, 24A is plenty for charging.
 

Adventureboy

Well-Known Member
First Name
Jonathan
Joined
Jan 5, 2024
Threads
1
Messages
455
Reaction score
315
Location
Ontario
Vehicles
2022 MME Premium AWD ER, 2023 Lightning Lariat ER, 2005 Volvo S60 T5 M66
Country flag
A 14-50 has to be fused to 50A (and would be better installed as 60A because it could be a continuous load but in either case the 42A charger is safe)
A NEMA 14-50 can ONLY be connected to a 50A breaker to be compliant. This will allow a continuous 40amp load (80%). Any higher loads like continuous 42A should kick out the 50Amp breaker.
 

Adventureboy

Well-Known Member
First Name
Jonathan
Joined
Jan 5, 2024
Threads
1
Messages
455
Reaction score
315
Location
Ontario
Vehicles
2022 MME Premium AWD ER, 2023 Lightning Lariat ER, 2005 Volvo S60 T5 M66
Country flag
No it won’t. Breakers are designed to carry their rated load.
You can push it if you like - that is your choice. 80% capacity (40amp) is the design and code limit for a 50amp breaker. Your breaker may carry it, but it will heat up (try a laser thermometer on it or simply touch it if you are drawing 48amps for a few hours on a 50 amp breaker).
 

ChehRob

Well-Known Member
First Name
Rob
Joined
Aug 24, 2023
Threads
13
Messages
959
Reaction score
568
Location
Seattle WA
Vehicles
MME Premium AWD Ext. Range (Job2)
Occupation
ret
Country flag
Likely most of us should have an electrician evaluate existing wiring, breaker, breaker box and outlet. Any one of them can be a point of weakness, especially in wiring that was done decades ago.
 

mateo

Well-Known Member
Joined
Jul 28, 2022
Threads
7
Messages
243
Reaction score
365
Location
Chicago
Vehicles
2022 MME GT
Country flag
Likely most of us should have an electrician evaluate existing wiring, breaker, breaker box and outlet. Any one of them can be a point of weakness, especially in wiring that was done decades ago.
Agreed, although unfortunately a lot of that can be hidden behind walls. The horrors I've found when remodeling houses (all pre-1960s builds) I've lived at would give me pause to use existing wiring for EV charging. I ran brand new wiring for my charger.
 

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
34
Messages
5,689
Reaction score
8,069
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
You can push it if you like - that is your choice. 80% capacity (40amp) is the design and code limit for a 50amp breaker. Your breaker may carry it, but it will heat up (try a laser thermometer on it or simply touch it if you are drawing 48amps for a few hours on a 50 amp breaker).
I didn’t say anything like that. I simply conveyed how breakers work.
 

AKgrampy

Well-Known Member
First Name
Mike
Joined
Jan 29, 2022
Threads
7
Messages
3,523
Reaction score
3,592
Location
Fairbanks, Alaska
Vehicles
Ford Expedition, Ford F-150, Mach E GT
Occupation
Retired
Country flag
You just paid $45 - $65k on a new car. Do not cut corners on electrical. Number one issue is be safe. EV charging is a continuous high load which is different than most home loads. No need to go to the max (but I would if practical) but certainly ensure that what you do go with is safe and is not pushing the limits!
 

goodguy

Well-Known Member
First Name
j
Joined
Jun 23, 2023
Threads
0
Messages
69
Reaction score
58
Location
utah
Vehicles
ford
Country flag
Opinions vary... but many sources say you can use the stock provided cord with a 40 amp breaker and a NEMA 14-50 outlet that is signed to only allow 32 amp continuous max (40 max) and 8 AWG wire (as short as possible). The math works But I am sure others will say that the stock cord should not be used and the Nema 14-50 MUST be 50 amp. This is really no different than allow a 50 amp breaker to allow a 40 amps continuous load. Other than the fact that the Nema 14-50 outlet is rated at 50 amps, but you have limited it to 40 max. Thus the sign. Or better yet remove the outlet before selling the house. Again. not an electrician. Also i am talking about a new breaker.... not the dryer question. And why would you do this.... to save money. 8 AWG is cheaper than 6AWG.