Hi all,

I just had the electrician come in to install a 240v outlet for faster charging. His supplier didn't have the 50A breaker so he installed a 60A and will switch them out when he gets it back in stock. Do y'all know if the charger that came with the MME is limited to 48A like I've read online? Electrician said its safe, but I'm skeptical.
Sponsored

 
OP
OP
Bausmx5

Bausmx5

Member
First Name
Pez
Joined
Jun 27, 2021
Threads
4
Messages
24
Reaction score
38
Location
MD
Vehicles
‘21 Mustang Mach-E California, ‘14 Mazda MX-5
Occupation
Software Engineer
Country flag
He did install the Nema 14-50 outlet over 8/3 Romex (probably to save money). Its the 60 amp breaker I'm concerned about. I just don't want a fire
 

Garbone

Well-Known Member
First Name
Gary
Joined
Dec 16, 2020
Threads
31
Messages
1,201
Reaction score
1,666
Location
Florida
Vehicles
21 Mach E , 22 MachE, 62 C10 Big window long bed
Occupation
Loafer
Country flag
Depends on the type of "Romex". #6 THHN can do 60 amps. #8 can do 55,. Should be fine. When I went to get my breaker there is a shortage due to a warehouse fire. Got the last one at my 3rd stop so it is a thing.

I would not worry about the 32 amp Ford charger burning you down.
 


HuntingPudel

Well-Known Member
First Name
Steve
Joined
Mar 23, 2021
Threads
65
Messages
8,061
Reaction score
9,624
Location
Bay Area, CA
Vehicles
2021 MME GT-PE, 1979 Fire-Am, 1972 K/5 Blazer
Occupation
Engineering
Country flag
You should be safe if you are using the included mobile charger, as long as nothing compromises insulation on its wiring. The other option is to not use the circuit until the breaker is replaced.
 

ARK

Well-Known Member
Joined
Aug 21, 2020
Threads
42
Messages
2,732
Reaction score
3,986
Location
Los Angeles
Vehicles
Mustang Mach E
Country flag
He did install the Nema 14-50 outlet over 8/3 Romex (probably to save money). Its the 60 amp breaker I'm concerned about. I just don't want a fire
The other responses are correct, the mobile charger that came with the car is limited to drawing 32 amps anyway. The Mach-E is capable of taking up to 48 amps, and the separate Ford Connected Charge Station that you can purchase can put out 48 amps, and I think that is the one you are thinking of.
 

Texas-E

Well-Known Member
Joined
May 16, 2021
Threads
8
Messages
284
Reaction score
483
Location
Texas
Vehicles
2021 Mach-E
Country flag
I'm not trying to scare you, but think for a minute about why you have a breaker in the first place. It isn't because you trust the device plugged in and the wiring. Should you be ok with the mobile charger that came with your car... yes.

The 48amp for something like the ChargePoint (that I have) requires a 60 amp breaker and wiring that is appropriate for a 60amp circuit. I'm surprised that a licensed electrician did that. The 14-50 plug should limit the risk, too.
 
OP
OP
Bausmx5

Bausmx5

Member
First Name
Pez
Joined
Jun 27, 2021
Threads
4
Messages
24
Reaction score
38
Location
MD
Vehicles
‘21 Mustang Mach-E California, ‘14 Mazda MX-5
Occupation
Software Engineer
Country flag
You should be safe if you are using the included mobile charger, as long as nothing compromises insulation on its wiring. The other option is to not use the circuit until the breaker is replaced.
I will probably just use the standard outlet for now until he comes back and replaces it. Luckily there’s a 150kw charger just down the street from me that I can use in the meantime
 

Sweetwater

Well-Known Member
Joined
Feb 5, 2020
Threads
14
Messages
500
Reaction score
345
Location
Ohio
Vehicles
Jeep
Occupation
Retired Electrician
Country flag
National Electrical Code
Allowable Ampacities of Insulated Conductors Rated 0-2000 Volts
As Excerpted from the 2002 National Electrical Code
Ampacities of Not More Than Three Current-Carrying Conductors in Raceway, Cable or Earth. Based on Ampbient Temperature of 30°C (86°F)
SIZE AWG OR kcmil
Ford Mustang Mach-E Electrician just installed a 60A breaker over 8/3 Romex 1625091836827
Ford Mustang Mach-E Electrician just installed a 60A breaker over 8/3 Romex 1625091836827
Copper Conductors
Temperature Rating of ConductorTemperature Rating of Conductor
60°C
TYPES
TW UF
#840 amps
Your electrician is wrong. Your cable is good for only 40 amps.
https://www.usawire-cable.com/pdf/nec-ampacities.pdf
 
OP
OP
Bausmx5

Bausmx5

Member
First Name
Pez
Joined
Jun 27, 2021
Threads
4
Messages
24
Reaction score
38
Location
MD
Vehicles
‘21 Mustang Mach-E California, ‘14 Mazda MX-5
Occupation
Software Engineer
Country flag
National Electrical Code
Allowable Ampacities of Insulated Conductors Rated 0-2000 Volts
As Excerpted from the 2002 National Electrical Code
Ampacities of Not More Than Three Current-Carrying Conductors in Raceway, Cable or Earth. Based on Ampbient Temperature of 30°C (86°F)
SIZE AWG OR kcmil
Ford Mustang Mach-E Electrician just installed a 60A breaker over 8/3 Romex 1625091836827
Ford Mustang Mach-E Electrician just installed a 60A breaker over 8/3 Romex 1625091836827
Copper Conductors
Temperature Rating of ConductorTemperature Rating of Conductor
60°C
TYPES
TW UF
#840 amps
Your electrician is wrong. Your cable is good for only 40 amps.
https://www.usawire-cable.com/pdf/nec-ampacities.pdf
I asked around on electrician forums, they all said 50A breakers are fine
 

dtbaker61

Well-Known Member
First Name
Dan
Joined
May 11, 2020
Threads
104
Messages
3,971
Reaction score
3,645
Location
santa fe,nm
Website
www.envirokarma.org
Vehicles
MME (delivered 2/26/21), DIY eMiata BEV
Occupation
Solar Sales/install
Country flag
He did install the Nema 14-50 outlet over 8/3 Romex (probably to save money). Its the 60 amp breaker I'm concerned about. I just don't want a fire
8/3 is cutting it very close if you were pulling the full 50amps... remember charging is a continuous load and solid wire will heat up a bit more than stranded. I'd recommend you replace the 60amp circuit breaker with a 40amp to prevent anybody or a future charger upgrade from pulling more than the wire can handle.

NEMA 14-50 outlet really should have #6 wire for L1, N, L2, and at least 10awg for ground with 50amp circuit. This type of wire can be separate cable in a conduit, or the direct bury flatwire some Electricians use for 50amp air conditioners.
 

Fat Mach

Well-Known Member
Joined
Dec 29, 2020
Threads
12
Messages
499
Reaction score
632
Location
Nor Cal
Vehicles
2013 GT350
Country flag
How long is the wire run? A couple feet, or to the other side of the house?
 

malba2366

Well-Known Member
Joined
Dec 7, 2019
Threads
7
Messages
448
Reaction score
427
Location
NY
Vehicles
911 C2S
Country flag
Your electrician is incompetent. He should have used 6/3 wire. Putting a 60 AMP breaker is a problem because 60 amps through 8/3 is a fire hazard, even though the charger is only supposed to draw 32 amps, the breaker is the safeguard incase it tries to draw more due to a fault.