Ground Up or Down for Nema Plug 14-15 Installation?

barryvo

Well-Known Member
First Name
Barry
Joined
Jun 9, 2021
Threads
12
Messages
137
Reaction score
94
Location
Las Vegas, Nevada
Vehicles
VW Passat and Jeep Cherokee
Country flag
My electrician is asking whether to install the nema 14-50 with the ground up or down.

We plan on using the Ford Mobile Charger at first but may upgrade to a ChargePoint or WallBox in the future.

Any recommendations for up or down?
Sponsored

 

OttawaGuy

Well-Known Member
Joined
Nov 15, 2020
Threads
27
Messages
647
Reaction score
811
Location
Gatineau, Canada
Vehicles
Mach E RWD SR, F150 XLT Special Edition
Occupation
Busy!
Country flag
Look at our your plug (for the charger is down), the Ford mobile one is better suited for a ground up (that's what Ford recommends) since it will be hanging below the outlet. If you are thinking of using it backwards (head down) then put the ground down.

Then on your future charger, what's most "convenient" and doesn't require the cable to be twisted to accommodate the other way around. But in the end, you could simply turn the breaker off and turn the outlet around if needed.

Also check your building code (well your electrician should do that), there may be some requirements on how to put the ground in your area.
 

Benny’66

Well-Known Member
Joined
May 13, 2021
Threads
4
Messages
318
Reaction score
402
Location
NY
Vehicles
1966 Mustang, 2021 Mach E GTPE
Occupation
Plant Manager
Country flag
My electrician is asking whether to install the nema 14-50 with the ground up or down.

We plan on using the Ford Mobile Charger at first but may upgrade to a ChargePoint or WallBox in the future.

Any recommendations for up or down?
The ground should always be up. Which is counter intuitive because most house plugs have the ground hole down and that is how we are used to seeing them. Maybe because it makes a happy face that way. As my electrical engineering brother explained to me many years ago, the ground should always be up. Two main reasons: #1. The ground is always slightly longer so that it enters and makes contact with the receiver plug circuit first. If the plug is mounted lower to the ground, say less than 3’ from the ground, humans have a tendency to not bend over so when you plug in an appliance, you are actually canting the male plug and negating the extended ground feature if the “positive” terminals are on top. #2. Which is especially important in a garage, if the plug comes out of the wall receptacle slightly and something were to slide down the wall and make contact, you want the ground lug to prevent that item from arcing the power leads. Which it would do if it were on top and gravity stays the way it is.

Now, if your mount your plug at eye level, these concerns are lessened, but #2 is always a concern (gravity still).

I run a manufacturing plant and ALL plugs are installed with the ground up, even in the offices. Which is why all plugs that I have installed at my house are also that way.
 

machefan

Well-Known Member
Joined
Jan 14, 2020
Threads
25
Messages
1,709
Reaction score
2,433
Location
NJ
Vehicles
RR FE 21', Leaf 18' and Bronco BadLands 2022
Occupation
IT
Country flag
I run a manufacturing plant and ALL plugs are installed with the ground up, even in the offices. Which is why all plugs that I have installed at my house are also that way.
Most commercial is up, not sure if it's a code thing but for sure a trades thing.

The answer to the question is based on the charger being used, I have the Ford supplied one and for sure ground up with it.

Screen Shot 2021-06-18 at 8.23.26 AM.png
 
OP
OP

barryvo

Well-Known Member
First Name
Barry
Joined
Jun 9, 2021
Threads
12
Messages
137
Reaction score
94
Location
Las Vegas, Nevada
Vehicles
VW Passat and Jeep Cherokee
Country flag
I appreciate the replies and will go with the ground up since I'm going to start off with the Ford Mobile Charger. I'll try try and research WallBox and ChargePoint and strive to get a unit best setup for ground up.

I am learning a lot and should be ready for the MME in December.
 


timbop

Well-Known Member
First Name
Tim
Joined
Jan 3, 2020
Threads
63
Messages
6,740
Reaction score
13,782
Location
New Jersey
Vehicles
Solar powered 2021 MME ER RWD & 2022 Corsair PHEV
Occupation
Software Engineer
Country flag
It depends on the charger. The ford mobile charger is better with the ground up as one usually installs the charger hanging down. For some reason the Grizzl-E is wired the other way, as are some of the other chargers. Decide on the charger you are going to buy and orient the ground accordingly
 
OP
OP

barryvo

Well-Known Member
First Name
Barry
Joined
Jun 9, 2021
Threads
12
Messages
137
Reaction score
94
Location
Las Vegas, Nevada
Vehicles
VW Passat and Jeep Cherokee
Country flag
It depends on the charger. The ford mobile charger is better with the ground up as one usually installs the charger hanging down. For some reason the Grizzl-E is wired the other way, as are some of the other chargers. Decide on the charger you are going to buy and orient the ground accordingly
Is there an easy way to tell which way the charger is setup for before purchasing? We are leaning towards the WallBox or ChargePoint.
 

BMT1071

Well-Known Member
First Name
Mike
Joined
Mar 21, 2021
Threads
61
Messages
3,098
Reaction score
4,248
Location
Glendale, AZ
Vehicles
21 MME SR RWD, 23 MME GTPE
Occupation
Machine Control Specialist
Country flag
Is there an easy way to tell which way the charger is setup for before purchasing? We are leaning towards the WallBox or ChargePoint.
For the CPHF you want the ground up. See, that was easy. ??

20210401_151616.jpg


20210403_114334.jpg
 

GW Shark

Well-Known Member
First Name
Larry
Joined
Jun 2, 2021
Threads
11
Messages
314
Reaction score
352
Location
South Carolina
Vehicles
2021 Premium ER AWD Star White, 2014 Prius V
Occupation
Scuba Instructor
Country flag
I am 95% ignorant regarding wiring but I have to ask - What about ground sideways?
 

phidauex

Well-Known Member
First Name
Sam
Joined
Dec 8, 2020
Threads
16
Messages
844
Reaction score
1,548
Location
Colorado
Vehicles
2021 MachE 4EX, 2006 Prius, 1997 Tacoma
Occupation
Renewable Energy Engineer
Country flag
I am 95% ignorant regarding wiring but I have to ask - What about ground sideways?
The NEC, and I suspect it’s counterpart in Canada, does not dictate orientation of receptacles so you can go nuts. 45 degrees and keep em guessing!

EDIT: To be prudent, I’ll note that outdoor enclosures and weatherproof boxes usually DO have a required orientation, and the code requires you to follow the installation instructions, so that may limit some sideways applications outdoors!
 
Last edited:

idkhow

Banned
Banned
First Name
Bateman
Joined
Jun 12, 2021
Threads
10
Messages
219
Reaction score
251
Location
Jersey
Vehicles
2021 mach-e premium, van down by the river
Occupation
it plumber, auto detailer
Country flag
Most commercial is up, not sure if it's a code thing but for sure a trades thing.
It's a trade thing, no where in the NEC code at all, don't let others BS and tell you it is. This was as of 2017, I read the thing to upgrade our NJ 1950's cape.

Ground up installs are the tell-tale sign of someone who's done a commercial or hospital install.

They are mounted ground up in hospitals so that if it's dislodged a bit, and something drapes across it (think a busy room during surgery) it will hit the ground first and not arc.

With the weight of these plugs, there's no reason why ground down isn't fine.

I personally use Leviton SmartLock Dual AFCI / GFCI outlets at every home-run outlet. Any outlets added need to have AFCI (arc fault current interrupter) now per NEC code, depending on what year your state is running on.

Judging as this will likely be a single drop, you would need a GFCI breaker in the box for maximum protection, and just install the ground down.

Otherwise you end up with the hot and neutral plugs becoming what 'holds the plug in' - not gravity against a ground plug. With that much wattage flowing through, unless it's mounted in place you'll have a wizards sleeve situation in a few years with the plug getting loose.

A waterproof box + ground down is just fine. If you want extra protection, get a GFCI breaker for the run.
 

Jeffvisor

Well-Known Member
First Name
Jeff
Joined
Feb 24, 2021
Threads
30
Messages
718
Reaction score
653
Location
Harrisburg, PA
Vehicles
Ford Mustang Mach-e
Occupation
Retired
Country flag
Is there an easy way to tell which way the charger is setup for before purchasing? We are leaning towards the WallBox or ChargePoint.
I have the Wallbox and it has the ground down but I had the electrian install ground up and curve the cord and it works great. I always heard install outlet ground up for the reasons explained earlier in the thread if something slides down you want it to hit the ground not the live wires.
 

idkhow

Banned
Banned
First Name
Bateman
Joined
Jun 12, 2021
Threads
10
Messages
219
Reaction score
251
Location
Jersey
Vehicles
2021 mach-e premium, van down by the river
Occupation
it plumber, auto detailer
Country flag
What about ground sideways?
Nothing in the NEC about that, our outdoor waterproof receptacles I did are mounted horizontal. I went a little overboard and installed dual AFCI / GFCI outlets at every outlet, not just the home-run.


Happened after I went around with a tester and found out our sink GFCI and outdoor GFCI near a hose were seized open (providing power) - Now I use the SmartLockPro's that test themselves 100 times per second with a little green light to show you all is well.

Better yet, they will not power on if they've encountered a serious threat.

If it's an outdoor install, AFCI isn't necessary and my product of choice of theirs is a SmartLockPro GFCI slim (slim is crucial for 1950's era outlet boxes) - they are GFCI with weather resistance.

If you need GFCI 110V for interior, exterior, get one of these and you're set for years. All outlets down line from it are protected as well from the first (home-run) outlet
 

timbop

Well-Known Member
First Name
Tim
Joined
Jan 3, 2020
Threads
63
Messages
6,740
Reaction score
13,782
Location
New Jersey
Vehicles
Solar powered 2021 MME ER RWD & 2022 Corsair PHEV
Occupation
Software Engineer
Country flag
ground pin up assuming the charger is mounted above the plug. IMHO it is generally better not to have a 180 degree bend in a short and thick cable like that:

Ford Mustang Mach-E Ground Up or Down for Nema Plug 14-15 Installation? 1624046858368
 

timbop

Well-Known Member
First Name
Tim
Joined
Jan 3, 2020
Threads
63
Messages
6,740
Reaction score
13,782
Location
New Jersey
Vehicles
Solar powered 2021 MME ER RWD & 2022 Corsair PHEV
Occupation
Software Engineer
Country flag
The NEC, and I suspect it’s counterpart in Canada, does not dictate orientation of receptacles so you can go nuts. 45 degrees and keep em guessing!

EDIT: To be prudent, I’ll note that outdoor enclosures and weatherproof boxes usually DO have a required orientation, and the code requires you to follow the installation instructions, so that may limit some sideways applications outdoors!
Right, but the screw attachments to the outlet are at the top and bottom and studs run vertical, so unless you go out of your way to mount the box sideways the choice is top or bottom.