I watched the video where "industrial grade NEMA 14-50" plugs were catching fire because of lesser quality than the Hubbell connector. So I opted to replace mine with a Hubbell after 16 months of ownership. My original plug was installed by an electrician and has worked fine for 16 months.

To my surprise, when I went to pull out the original plug, it had only 3 wires. There was a ground and two black wires. Nothing was connected to the neutral connector where the white wire should go.

My question is: Do I need an electrician to come out again and install the neutral? Or can I just go along with the way it has worked since the beginning?
Sponsored

 

Garbone

Well-Known Member
First Name
Gary
Joined
Dec 16, 2020
Threads
31
Messages
1,202
Reaction score
1,666
Location
Florida
Vehicles
21 Mach E , 22 MachE, 62 C10 Big window long bed
Occupation
Loafer
Country flag
No
 

HuntingPudel

Well-Known Member
First Name
Steve
Joined
Mar 23, 2021
Threads
65
Messages
8,064
Reaction score
9,626
Location
Bay Area, CA
Vehicles
2021 MME GT-PE, 1979 Fire-Am, 1972 K/5 Blazer
Occupation
Engineering
Country flag
There are no EVSEs that use the Neutral wire, so itā€™s not necessary. It's really only necessary if you want to pull 115/120V out of the outlet. Thatā€™s highly unlikely since you will probably only use the circuit for the EVSE. Since EVSEs donā€™t use the neutral, I have wondered why so many manufacturers settled on the 14-50p on their units rather than the 6-50p. Toe-MAY-toe, toe-MAH-toeā€¦ šŸ˜ŠšŸ©
 

timbop

Well-Known Member
First Name
Tim
Joined
Jan 3, 2020
Threads
63
Messages
6,729
Reaction score
13,758
Location
New Jersey
Vehicles
Solar powered 2021 MME ER RWD & 2022 Corsair PHEV
Occupation
Software Engineer
Country flag
The neutral line is only needed if the EVSE requires 120V as well as 240V, which I assume isn't typically necessary. I would say the EVSE you have (and probably the vast majority) don't need it.
 

timbop

Well-Known Member
First Name
Tim
Joined
Jan 3, 2020
Threads
63
Messages
6,729
Reaction score
13,758
Location
New Jersey
Vehicles
Solar powered 2021 MME ER RWD & 2022 Corsair PHEV
Occupation
Software Engineer
Country flag
There are no EVSEs that use the Neutral wire, so itā€™s not necessary. It's really only necessary if you want to pull 115/120V out of the outlet. Thatā€™s highly unlikely since you will probably only use the circuit for the EVSE. Since EVSEs donā€™t use the neutral, I have wondered why so many manufacturers settled on the 14-50p on their units rather than the 6-50p. Toe-MAY-toe, toe-MAH-toeā€¦ šŸ˜ŠšŸ©
Probably because the 14-50 is much more prevalent
 


HuntingPudel

Well-Known Member
First Name
Steve
Joined
Mar 23, 2021
Threads
65
Messages
8,064
Reaction score
9,626
Location
Bay Area, CA
Vehicles
2021 MME GT-PE, 1979 Fire-Am, 1972 K/5 Blazer
Occupation
Engineering
Country flag
Probably because the 14-50 is much more prevalent
But it wasnā€™t when I bought my EVSE. Back then, it was a pretty fair split between the two standards. Maybe they felt the ā€ovenā€ plug/receptacle were better suited than the ā€œwelderā€ plug/receptacle at some point. My 6-50r consumer-grade outlet has been just fine for nearly a decade though. šŸ¤·ā€ā™‚ļøšŸ©
 

Mach-Lee

Well-Known Member
First Name
Lee
Joined
Jul 16, 2021
Threads
204
Messages
7,732
Reaction score
15,308
Location
Wisconsin
Vehicles
2022 Mach-E Premium AWD
Occupation
Sci/Eng
Country flag
The EVSE doesn't need the neutral wire, but technically a 14-50 receptacle has to have a neutral connected by code. I wouldn't worry about the neutral if you know the outlet will only ever be used for an EVSE.
 

bshaw

Well-Known Member
Joined
May 18, 2020
Threads
12
Messages
1,280
Reaction score
1,712
Location
Boston, MA
Vehicles
2021 Mustang Mach E 4X (Job 1)
Country flag
I believe an RV is a common example of something that will expect to find a neutral wire in a 14-50 outlet.
 

Mach-Lee

Well-Known Member
First Name
Lee
Joined
Jul 16, 2021
Threads
204
Messages
7,732
Reaction score
15,308
Location
Wisconsin
Vehicles
2022 Mach-E Premium AWD
Occupation
Sci/Eng
Country flag
There are no EVSEs that use the Neutral wire, so itā€™s not necessary. It's really only necessary if you want to pull 115/120V out of the outlet. Thatā€™s highly unlikely since you will probably only use the circuit for the EVSE. Since EVSEs donā€™t use the neutral, I have wondered why so many manufacturers settled on the 14-50p on their units rather than the 6-50p. Toe-MAY-toe, toe-MAH-toeā€¦ šŸ˜ŠšŸ©
I think there will be a shift back towards 6-50 once 240V EV outlets are required in new houses by code. 6-50 saves some copper, and electricians are cheap bastards when it comes to new home wiring so they will do it to save a couple bucks.
 

chrisGT

Well-Known Member
First Name
Chris
Joined
Oct 12, 2021
Threads
3
Messages
325
Reaction score
460
Location
Northern California
Vehicles
2021 Ford Mach-e GT
Country flag
I guess the installation wasn't inspected by city otherwise they should have caught the missing neutral.
I suggest that you try have the original electrician come back run a neutral because their work does not meet the electrical code and they practically "cheated" you by saving wire cost.
 

RickMachE

Well-Known Member
Joined
Jul 1, 2021
Threads
200
Messages
13,135
Reaction score
17,856
Location
SE MI
Vehicles
2022 Mach-E Premium 4X, 2022 Lightning Lariat
Country flag
I had my electrician wire my hardwired JuiceBox, and insisted they use 4 conductor wire. I have an unconnected neutral in my box, so I can connect a standard 4 conductor 14-50 in the future.
 

HuntingPudel

Well-Known Member
First Name
Steve
Joined
Mar 23, 2021
Threads
65
Messages
8,064
Reaction score
9,626
Location
Bay Area, CA
Vehicles
2021 MME GT-PE, 1979 Fire-Am, 1972 K/5 Blazer
Occupation
Engineering
Country flag
I think there will be a shift back towards 6-50 once 240V EV outlets are required in new houses by code. 6-50 saves some copper, and electricians are cheap bastards when it comes to new home wiring so they will do it to save a couple bucks.
LOL *I* am a cheap bastard. Perhaps because of my Asian Redneck Poodle upbringing. šŸ¤ŖšŸ©
 

timbop

Well-Known Member
First Name
Tim
Joined
Jan 3, 2020
Threads
63
Messages
6,729
Reaction score
13,758
Location
New Jersey
Vehicles
Solar powered 2021 MME ER RWD & 2022 Corsair PHEV
Occupation
Software Engineer
Country flag
But it wasnā€™t when I bought my EVSE. Back then, it was a pretty fair split between the two standards. Maybe they felt the ā€ovenā€ plug/receptacle were better suited than the ā€œwelderā€ plug/receptacle at some point. My 6-50r consumer-grade outlet has been just fine for nearly a decade though. šŸ¤·ā€ā™‚ļøšŸ©
But I believe it was certainly much more common in campgrounds (@JamieGeek can confirm that) and in general in homes for appliances - I can't say I've ever seen a 6-50 in person in any home/apartment I've been in, although that isn't a very large sample size. For point of reference I've redone the kitchen in both houses I've owned and worked for a time for my brother's general contracting business.
 

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
30
Messages
4,403
Reaction score
6,093
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
Itā€™s not a code violation to not have the neutral on a 14-50 unless there is another 14-50 on the premesis with a neutral. (Section 406.8 requires all configurations of an outlet to have interchangeability).

But itā€™s probably not a good idea.
 

JamieGeek

Well-Known Member
Joined
Dec 29, 2019
Threads
82
Messages
3,556
Reaction score
6,746
Location
Southeastern Michigan
Website
spareelectrons.wordpress.com
Vehicles
Mach-E, old: Bolt, C-Max Energi, Focus Electric
Country flag
But I believe it was certainly much more common in campgrounds (@JamieGeek can confirm that) and in general in homes for appliances - I can't say I've ever seen a 6-50 in person in any home/apartment I've been in, although that isn't a very large sample size. For point of reference I've redone the kitchen in both houses I've owned and worked for a time for my brother's general contracting business.
14-50's are in campgrounds because the RV's that use them have two A/C's: Each wired to one leg of the 120V provided--they don't actually use 240V between the two hots.

When the electrician wired our house for an EVSE back in 2013 he did a 6-50.