Fried 60A Circuit Breaker

jpblincoln

Active Member
First Name
John
Joined
Jan 1, 2021
Threads
1
Messages
42
Reaction score
51
Location
20817
Vehicles
2021 Mach E
Occupation
Manager
Country flag
I have a Ford Connected 48A charger that I run at 42 amps. Over the past three years, I've fried two 60A Eaton Cutler-Hammer style circuit breakers. This time, I'm purchasing the actual Eaton brand, as I suspect the previous ones were Eaton CH clones. I also plan to reduce the current to 36 amps. When the breaker dies the blue charger light turns off, and there’s no 240V across the terminals. Has anyone else experienced similar issues?
Sponsored

 

phidauex

Well-Known Member
First Name
Sam
Joined
Dec 8, 2020
Threads
17
Messages
967
Reaction score
1,843
Location
Colorado
Vehicles
2021 MachE 4EX, 2006 Prius, 1997 Tacoma
Occupation
Renewable Energy Engineer
Country flag
It is possible for breakers to fail like anything else mechanical, but two in a row is suspicious. Do they look tripped, but won't reset?

Trying another model makes sense, breakers are supposed to work continuously, but most manufacturers know that a breaker will almost never be at its full continuous rating, so many aren't very robust for extended full power use.
 

Tomm

Well-Known Member
First Name
Tom
Joined
Apr 20, 2024
Threads
5
Messages
248
Reaction score
221
Location
Davis Ca
Vehicles
2023 Premium
Occupation
Surgeon
Country flag
I would hire an electrician to take a look. I wired my own, but it works and has not fried the breaker. If it does, I will get an electrician.
 


Scooby24

Well-Known Member
First Name
Greg
Joined
Jul 2, 2021
Threads
29
Messages
2,123
Reaction score
3,296
Location
Olathe, KS
Vehicles
'25 BMW i4 M50; '25 MME GT
Occupation
Healthcare IT
Country flag
When I installed mine (with an electrician friend) I bought a torque screwdriver to be sure both the breaker and the receptacle had the properly rated torque levels on the screws and I was legit SHOCKED at how much torque that actually was. My Receptacle is a Cooper (Now Eaton) 5754N which is phillips head screw and couldn't take as much as the Hubbell or Byrant but at 25 inch lbs, before I got the torque screwdriver out I thought I had torqued it enough...but not even close. It took a LOT more than I thought. Thought for sure I was stripping it.

Then when we got to the breaker, for 6awg it was 40 inch lbs. That felt like a hell of a lot.

For 60 amp I'm assuming you should have used 4 awg copper and that would have needed 45 inch lbs. If you used aluminum I think that would have had to be 3 awg, 50 inch lbs.
 

AZBill

Well-Known Member
First Name
Bill
Joined
May 26, 2021
Threads
12
Messages
1,990
Reaction score
2,318
Location
Arizona
Vehicles
MME CA Route 1, Hummer EV SUT, Escalade IQ
Occupation
Retired
Country flag
I had had 60A breaker to my pool equipment sub panel melt down and fail several years ago. More recently had one leg of a 125A breaker going to my detached garage fail. Both were Eaton. Too much of this junk is poorly made in China.
 

Old_Norm

Well-Known Member
Joined
Jan 14, 2023
Threads
58
Messages
869
Reaction score
1,069
Location
Columbus Ohio
Vehicles
2023 MME Select EAWD, 2023 Maverick Lariat LUX
Occupation
Retired
Country flag

Mach-Lee

Well-Known Member
First Name
Lee
Joined
Jul 16, 2021
Threads
262
Messages
11,366
Reaction score
25,028
Location
Wisconsin
Vehicles
2022 Mach-E Premium AWD
Occupation
Sci/Eng
Country flag
I have a Ford Connected 48A charger that I run at 42 amps. Over the past three years, I've fried two 60A Eaton Cutler-Hammer style circuit breakers. This time, I'm purchasing the actual Eaton brand, as I suspect the previous ones were Eaton CH clones. I also plan to reduce the current to 36 amps. When the breaker dies the blue charger light turns off, and there’s no 240V across the terminals. Has anyone else experienced similar issues?
Where are you getting these breakers from? If you're buying them online for the cheapest price, there's a decent chance they're counterfeit. Always buy electrical devices from a brick and mortar store like Home Depot or trusted electrical supply houses. Type CH with the tan handles.

Like others say, you also need to check the bus bar the breaker stabs into. If that's damaged, then it will continue to cause overheating and further damage.

Torque the screws to spec, then loosen and torque them to spec again. This helps "settle" the strands and reduces loosening over time. If the copper is heat damaged, it needs to be cut back so fresh bright copper is exposed and used for the connection.

If it can't handle the full 48A all night long, something is wrong and needs investigating. Lowering the amperage is just a band-aid and should not be a long term fix.
 
Last edited:

Adventureboy

Well-Known Member
First Name
Jonathan
Joined
Jan 5, 2024
Threads
1
Messages
455
Reaction score
315
Location
Ontario
Vehicles
2022 MME Premium AWD ER, 2023 Lightning Lariat ER, 2005 Volvo S60 T5 M66
Country flag
If it can't handle the full 48A all night long, something is wrong and needs investigating. Lowering the amperage is just a band-aid and should not be a long term fix.
^^^^ This ^^^^

I've had to replace 1 breaker in 3 years. 50A on 40A EVSE. Nothing wrong with the wiring or torque, it just gave up and wouldn't reset. The breaker was about 15 years old and had run my welder periodically. It didn't handle the constant power draw from an EVSE for more than a few months. Good brand name replacement from an electrical supply shop has been running daily now for 2.5 years across 2 EVs.
 

ChasingCoral

Well-Known Member
First Name
Mark
Joined
Feb 3, 2020
Threads
502
Messages
14,318
Reaction score
28,675
Location
Maryland
Vehicles
2021 GB E4X FE, 2022 F-150 Lightning Lariat ER
Occupation
Retired oceanographer
Country flag
Open up the junction box where your EVSE is connected. Check for signs or loose wires or charred connections. If your EVSE is plugged in, check the connection of the plug in the receptacle.
 

johnnycombo

Well-Known Member
First Name
John
Joined
Jul 15, 2021
Threads
9
Messages
475
Reaction score
453
Location
Pennsylvania
Vehicles
Mustang Mach-E
Country flag
I have a ChargePoint hardwired and a 14-50 receptacle for my Grizzl-E mini. With the recommended wire at ”that time” my ChargePoint was set to 48 amps and the 14-50 limited to 40amps charging. On doing research for installing an industrial duty 14-50 , I also found the romex wire has also been downgraded for evse use. So instead of rewiring I lowered my breaker amps on both circuits and my ChargePoint is now set at 40amps and the Grizzl-E 32amps with new industrial 14-50. Also with all the extra stress we see with EV charging I used Noalox on all of my copper connections (absolutely no aluminum). It does two things , protects from corrosion and lubricates the connection for a better torque. For years I’ve had campers and always use Deoxit D100L on my RVs plugs, so now I’m using it on my evse plug.
 
Last edited:

Jtbuster

Well-Known Member
First Name
Brian oConnor
Joined
May 7, 2022
Threads
6
Messages
278
Reaction score
156
Location
Calif
Vehicles
Mach e
Country flag
When I installed mine (with an electrician friend) I bought a torque screwdriver to be sure both the breaker and the receptacle had the properly rated torque levels on the screws and I was legit SHOCKED at how much torque that actually was. My Receptacle is a Cooper (Now Eaton) 5754N which is phillips head screw and couldn't take as much as the Hubbell or Byrant but at 25 inch lbs, before I got the torque screwdriver out I thought I had torqued it enough...but not even close. It took a LOT more than I thought. Thought for sure I was stripping it.

Then when we got to the breaker, for 6awg it was 40 inch lbs. That felt like a hell of a lot.

For 60 amp I'm assuming you should have used 4 awg copper and that would have needed 45 inch lbs. If you used aluminum I think that would have had to be 3 awg, 50 inch lbs.
6 awp thhp is what is spec.
 

hprose

Well-Known Member
First Name
Harvey
Joined
May 17, 2022
Threads
0
Messages
239
Reaction score
154
Location
Pinellas Park FL
Vehicles
F250 and a Mach-e on order
Occupation
Financial Advisor
Country flag
I have a Ford Connected 48A charger that I run at 42 amps. Over the past three years, I've fried two 60A Eaton Cutler-Hammer style circuit breakers. This time, I'm purchasing the actual Eaton brand, as I suspect the previous ones were Eaton CH clones. I also plan to reduce the current to 36 amps. When the breaker dies the blue charger light turns off, and there’s no 240V across the terminals. Has anyone else experienced similar issues?
You need #6 wire. Nothing smaller. I noted the my 6-50 receptacle was melting one of the slots. That was causing a problem on my plugs. The receptacle was 20 years old. I replaced it with a $50 unit from Grainger that had a creamic heat sink rather than the plastic on the $10 units. Problem solved. The plug is also used for a kiln. I only unplug and plug in with the circuit breaker off.