Is This Sufficient?

Fatawan

Well-Known Member
Joined
Mar 9, 2021
Threads
3
Messages
63
Reaction score
53
Location
NC
Vehicles
2021 F-250 Tremor, 2021 Mach-E GT
Country flag
When I had our house built, the electrician wired the garage for what he said was a "standard 50A charger." I have attached a pic of what is behind the cover plate. The breaker in the panel is a 40A breaker. Is this wire sufficient for a 50A circuit if I changed the breaker in the panel? Do you see any reason he would have put just a 40A breaker in the box?

Ford Mustang Mach-E Is This Sufficient? wires
Sponsored

 

Clydesdale

Active Member
First Name
Chris
Joined
Mar 4, 2021
Threads
0
Messages
38
Reaction score
81
Location
Chicago
Vehicles
BMW M Roadster. Chevy Tahoe. Tesla model3.
Country flag
When I had our house built, the electrician wired the garage for what he said was a "standard 50A charger." I have attached a pic of what is behind the cover plate. The breaker in the panel is a 40A breaker. Is this wire sufficient for a 50A circuit if I changed the breaker in the panel? Do you see any reason he would have put just a 40A breaker in the box?

wires.webp
What gauge wire is it? Are there any marking on the sheathing? Also how far from the breaker is the outlet?
 

Jimrpa

Well-Known Member
First Name
Jim
Joined
Sep 10, 2020
Threads
297
Messages
9,595
Reaction score
12,936
Location
Wayne, PA
Vehicles
2021 Infinite Blue Premium Mustang Mach E ER AWD
Occupation
Retied (formerly tried to herd highly technical, independent cats)
Country flag
40A breaker will only support a maximum 32A load, per standard practice and most codes. Invite him back for a redo. While you’re at it, ask him where he gets his 62.5A breakers ?
 

goldriver

Member
First Name
BRUNO
Joined
Mar 4, 2021
Threads
4
Messages
20
Reaction score
18
Location
Québec
Vehicles
F-250 PS 2022, MACH-E PREMIUM 2021
Occupation
CONTRACTOR
Country flag
Can you see any mention on the wire lie 3/10 or 3/8 ? it would be written on the outside skin of the wire (if you have an acces at electrical panel side you'll probably have a better view of the outside wire skin)

with the attached picture it is hard to know the size of the wire (it could be a 10, 8 or ???)
 

ocdxfv

Well-Known Member
First Name
Matt
Joined
Feb 11, 2021
Threads
19
Messages
250
Reaction score
329
Location
Orange County, CA
Vehicles
2021 Mach E, 2013 Toyota Rav4 EV
Occupation
Retired radiology tech
Country flag
Can you see any mention on the wire lie 3/10 or 3/8 ? it would be written on the outside skin of the wire (if you have an acces at electrical panel side you'll probably have a better view of the outside wire skin)

with the attached picture it is hard to know the size of the wire (it could be a 10, 8 or ???)
The wire should have some markings on it. Take a photo of the wire markings and post it. My guess is that you have #8 wire (with a 40a breaker) and the wires probably say "THHN or THWN-2" or something similar.
 


OP
OP
Fatawan

Fatawan

Well-Known Member
Joined
Mar 9, 2021
Threads
3
Messages
63
Reaction score
53
Location
NC
Vehicles
2021 F-250 Tremor, 2021 Mach-E GT
Country flag
No markings on the wire in the outlet--I will open up the panel and check
 

ocdxfv

Well-Known Member
First Name
Matt
Joined
Feb 11, 2021
Threads
19
Messages
250
Reaction score
329
Location
Orange County, CA
Vehicles
2021 Mach E, 2013 Toyota Rav4 EV
Occupation
Retired radiology tech
Country flag
No markings on the wire in the outlet--I will open up the panel and check
When you open the panel, locate any other 240 volt breakers (dryer, oven, A/C, pool, etc) and visually compare the size of the wires. The 240v breakers should have bigger wire than the 120v breakers, and your 40a charger circuit should have bigger wires than the 30a and the same as any other 40a breakers.
 
OP
OP
Fatawan

Fatawan

Well-Known Member
Joined
Mar 9, 2021
Threads
3
Messages
63
Reaction score
53
Location
NC
Vehicles
2021 F-250 Tremor, 2021 Mach-E GT
Country flag
This is a subpanel on one end of the basement(long skinny house). The breaker in the main panel for this sub panel is 70A. The subpanel is within 20-25' of the outlet in the garage. The wires have no markings of any sort on them. It wasn't individual wires, but sheathed. The two breakers in the upper right are 30A and those wires are considerably smaller. The car charger breaker is lower left(sorry about the rotation!). If there is anything else I can get that might help, let me know. Thank you all.

Ford Mustang Mach-E Is This Sufficient? Wire1


Ford Mustang Mach-E Is This Sufficient? wire2


Ford Mustang Mach-E Is This Sufficient? wire3
 

CHeil402

Well-Known Member
First Name
Chris
Joined
Sep 21, 2020
Threads
8
Messages
726
Reaction score
1,325
Location
King of Prussia, PA
Vehicles
2017 Audi A4, 2021 MME
Occupation
Electrical Engineer
Country flag
This is a subpanel on one end of the basement(long skinny house). The breaker in the main panel for this sub panel is 70A. The subpanel is within 20-25' of the outlet in the garage. The wires have no markings of any sort on them. It wasn't individual wires, but sheathed. The two breakers in the upper right are 30A and those wires are considerably smaller. The car charger breaker is lower left(sorry about the rotation!). If there is anything else I can get that might help, let me know. Thank you all.

Wire1.jpg


wire2.webp


wire3.webp
Without knowing the gauge / makeup of the wire it's impossible to tell if the wire is properly sized for a 50 A breaker. Check out the table here which can answer your question if you can find the right row and column... https://www.wireandcabletips.com/what-is-ampacity/

Also, based on your description having that much downstream in the sub-panel from a 70 A breaker doesn't sound like a good idea (not unsafe, just prone to nuisance tripping of the 70 A upstream breaker). Ignoring all of the other 120 V circuits, I see a dryer and oven in there. If you ran the EVSE at the same time as the oven and/or dryer, that upstream 70 A breaker is likely to trip... that may be a reason your electrician installed only a 40 A breaker. Even if the wire is sized properly, you MAY run into issues pulling that much current from that one load in that sub-panel if you're running a bunch of other stuff at the same time.
 
OP
OP
Fatawan

Fatawan

Well-Known Member
Joined
Mar 9, 2021
Threads
3
Messages
63
Reaction score
53
Location
NC
Vehicles
2021 F-250 Tremor, 2021 Mach-E GT
Country flag
Sounds like I should just install a 14-50 plug and use the charging cable that comes with the car, or something like a Grizzle-E set to 32A. No reason to push the limits here. Thanks again.
 

CHeil402

Well-Known Member
First Name
Chris
Joined
Sep 21, 2020
Threads
8
Messages
726
Reaction score
1,325
Location
King of Prussia, PA
Vehicles
2017 Audi A4, 2021 MME
Occupation
Electrical Engineer
Country flag
Sounds like I should just install a 14-50 plug and use the charging cable that comes with the car, or something like a Grizzle-E set to 32A. No reason to push the limits here. Thanks again.
You might also want to put a label on the outlet that it's rated for 40 A and not 50 A since a NEMA 14-50 plug is supposed to be 50 A per code. Otherwise you (or someone in the future) might put something that draws the maximum from a NEMA 14-50 of 40 A which would result in annoying nuisance trips at best... or if the cable is actually only rated for 40 A and the CB tolerance is a little high an unsafe condition at worst.

Also... if you're having any nuisance trips, you can set the Grizzl-E to a lower current level so long as it meets your recharge rate needs. Most people don't actually need the full capabilities.
 

JCHLi

Well-Known Member
Joined
Jun 28, 2020
Threads
23
Messages
1,627
Reaction score
2,506
Location
Michigan
Vehicles
2021 Mustang Mach-E First Edition
Country flag
It's difficult the gauge the gauge of wire used. Do you have a set of dial calipers or inside micrometer?
 

ocdxfv

Well-Known Member
First Name
Matt
Joined
Feb 11, 2021
Threads
19
Messages
250
Reaction score
329
Location
Orange County, CA
Vehicles
2021 Mach E, 2013 Toyota Rav4 EV
Occupation
Retired radiology tech
Country flag
It's difficult the gauge the gauge of wire used. Do you have a set of dial calipers or inside micrometer?
Those look like #8 wires which are correct for the 40a breaker. I would NOT change the breaker to 50a. I would follow the previous suggestion of using the charger that came with the car AND labeling the outlet as "40 amp MAX, 32 amp continuous". Charging at 32 amps will serve you well.
 

JCHLi

Well-Known Member
Joined
Jun 28, 2020
Threads
23
Messages
1,627
Reaction score
2,506
Location
Michigan
Vehicles
2021 Mustang Mach-E First Edition
Country flag
Those look like #8 wires which are correct for the 40a breaker. I would NOT change the breaker to 50a. I would follow the previous suggestion of using the charger that came with the car AND labeling the outlet as "40 amp MAX, 32 amp continuous". Charging at 32 amps will serve you well.
You're eyes must be better calibrated then mine.
 
OP
OP
Fatawan

Fatawan

Well-Known Member
Joined
Mar 9, 2021
Threads
3
Messages
63
Reaction score
53
Location
NC
Vehicles
2021 F-250 Tremor, 2021 Mach-E GT
Country flag
Probably not exactly what you were after, but best I got!

Ford Mustang Mach-E Is This Sufficient? caliper