I’m running 220v to the garage - I was going to use and existing 40 amp breaker with 8 gauge wire.

I’d like NOT to buy a $700.00 charging station…will the charging devices Ford provide put 220v into the car?

So, will 40 amps / 8 gauge work? Or is 50 amp / 6 gauge required to work with Ford’s charging devices.?

thank you!
Sponsored

 

Davedough

Well-Known Member
First Name
Dave
Joined
Oct 12, 2020
Threads
14
Messages
1,812
Reaction score
4,266
Location
West BYGOD Virginia
Vehicles
Mach E GTPE , Explorer ST
Occupation
Federal IT Sales Engineer
Country flag
You need to account for overhead on the circuit. If you are hardwiring, I wouldn't go below a 60amp breaker personally. That's what I installed on mine because I read that that was what was recommended

Ford Mustang Mach-E 40 amp or 50 amp? 1647460898513
 

RickMachE

Well-Known Member
Joined
Jul 1, 2021
Threads
267
Messages
17,919
Reaction score
27,903
Location
SE MI
Vehicles
2022 Mach-E Premium 4X, 2022 Lightning Lariat ER
Country flag

ebeponyan

Well-Known Member
Joined
Mar 11, 2021
Threads
11
Messages
473
Reaction score
1,311
Location
Puget Sound
Vehicles
2021 Infinite Blue Mach-E Premium AWD ER
Country flag
You need to account for overhead on the circuit. If you are hardwiring, I wouldn't go below a 60amp breaker personally. That's what I installed on mine because I read that that was what was recommended

1647460898513.webp
By your own chart, a 40A breaker should be fine for the provided 32A Ford Mobile Charger.

You should be fine with 8 gauge, but if you're buying new wire anyway, I'd go for 6 gauge. You'll want a NEMA 14-50 outlet to plug into.

Edit with the disclaimer to always check local electrical code. A 50A breaker with 6 gauge is preferred, but it would be generally acceptable to have a 32A load on 8 gauge wire with a 40A breaker and a 14-50 outlet. Upgrading to 6 gauge is going to do more to future proof you, and I would personally feel more comfortable having a more robust circuit than technically required in this case.
 
Last edited:

SpaceEVDriver

Well-Known Member
Joined
Aug 26, 2021
Threads
71
Messages
2,651
Reaction score
4,774
Location
Arizona
Vehicles
2022 CA Route 1 AWD, ER; 2023 Lightning Lariat ER
Occupation
Planetary Science
Country flag
If you're planning to use the Ford Mobile Charger with its 240 Volt plug, then you need to install a NEMA 14-50 outlet. You should never connect a high amperage outlet to a lower amperage wire. The install requires 50 amp wiring and a 50 amp breaker. The breaker is not there to protect your equipment, it's there to protect your wiring and thus your house.

Don't put your entire house at risk because you want to save $50.
 


Mach-Lee

Well-Known Member
First Name
Lee
Joined
Jul 16, 2021
Threads
262
Messages
11,350
Reaction score
24,977
Location
Wisconsin
Vehicles
2022 Mach-E Premium AWD
Occupation
Sci/Eng
Country flag

Davedough

Well-Known Member
First Name
Dave
Joined
Oct 12, 2020
Threads
14
Messages
1,812
Reaction score
4,266
Location
West BYGOD Virginia
Vehicles
Mach E GTPE , Explorer ST
Occupation
Federal IT Sales Engineer
Country flag
By your own chart, a 40A breaker should be fine for the provided 32A Ford Mobile Charger.

You should be fine with 8 gauge, but if you're buying new wire anyway, I'd go for 6 gauge. You'll want a NEMA 14-50 outlet to plug into.

Edit with the disclaimer to always check local electrical code. A 50A breaker with 6 gauge is preferred, but it would be generally acceptable to have a 32A load on 8 gauge wire with a 40A breaker and a 14-50 outlet. Upgrading to 6 gauge is going to do more to future proof you, and I would personally feel more comfortable having a more robust circtuit than technically required in this case.
You're right. I was assuming it was like my ChargePoint and did 48A when hardwired
 

Mach-Lee

Well-Known Member
First Name
Lee
Joined
Jul 16, 2021
Threads
262
Messages
11,350
Reaction score
24,977
Location
Wisconsin
Vehicles
2022 Mach-E Premium AWD
Occupation
Sci/Eng
Country flag
If you're planning to use the Ford Mobile Charger with its 240 Volt plug, then you need to install a NEMA 14-50 outlet. You should never connect a high amperage outlet to a lower amperage wire. The install requires 50 amp wiring and a 50 amp breaker. The breaker is not there to protect your equipment, it's there to protect your wiring and thus your house.

Don't put your entire house at risk because you want to save $50.
NEC allows the use of a 50A receptacle on a 40A breaker, I see it all the time. Basically since a 40A receptacle doesn’t exist, you are allowed to go one size bigger. This is also why the mobile charger is set to 32A, so it can be used on 40A 14-50 circuits.


Thanks all! 50 amp, 6 gauge it will be.

…and a trip back to return 8gauge / 40 amp….
See above, you are fine doing 8 ga 40A if you don’t want to pay more.
 

Triggerhappy007

Well-Known Member
Joined
Feb 20, 2021
Threads
10
Messages
901
Reaction score
814
Location
TX
Vehicles
23 Premium, 3rd Mach-E
Country flag
NEC allows the use of a 50A receptacle on a 40A breaker, I see it all the time. Basically since a 40A receptacle doesn’t exist, you are allowed to go one size bigger. This is also why the mobile charger is set to 32A, so it can be used on 40A 14-50 circuits.




See above, you are fine doing 8 ga 40A if you don’t want to pay more.
What happens if you sell your house and the new buyer sees a 14-50 outlet in the garage and plugs in their 40A EVSE?
 

Mach-Lee

Well-Known Member
First Name
Lee
Joined
Jul 16, 2021
Threads
262
Messages
11,350
Reaction score
24,977
Location
Wisconsin
Vehicles
2022 Mach-E Premium AWD
Occupation
Sci/Eng
Country flag
What happens if you sell your house and the new buyer sees a 14-50 outlet in the garage and plugs in their 40A EVSE?
That’s their fault for not checking the breaker size during installation. You would not be liable since you’re following code.
 
 







Top