ChargePoint Users Step in

jdunc87

Well-Known Member
First Name
Josh
Joined
May 18, 2021
Threads
10
Messages
181
Reaction score
251
Location
Columbus, OH
Vehicles
21 Mach E GT PE, 20 Mustang GT 401A PP1, 21 F150
Occupation
make stuff go faster
Country flag
Just had my ChargePoint installed. It’s installed on a 70a breaker. It’s only charging currently under 12kw…. And about 29 miles/hr. Is something wrong? Or is this normal?

Ford Mustang Mach-E ChargePoint Users Step in D6E97B53-926C-495F-9CF4-822BA6D26BD4
Sponsored

 

generaltso

Well-Known Member
Joined
Jun 24, 2020
Threads
76
Messages
15,389
Reaction score
28,696
Location
Vermont
Vehicles
2024 Kia EV9 GT-Line
Country flag
The charger in the MME maxes out at 48A, which is about 11.5kW at 240V. Were you expecting something else?

Even if the MME could go higher, the ChargePoint Home Flex maxes out at 50A, so that would be a 12kW limit.
 

DevSecOps

Well-Known Member
First Name
Todd
Joined
Sep 22, 2021
Threads
69
Messages
4,764
Reaction score
11,624
Location
Sacramento, CA
Vehicles
'21 Audi SQ5 / '23 Rivian R1T / '23 M3P
Occupation
CISO
Country flag
Last edited:

scoopman

Well-Known Member
Joined
Jan 30, 2021
Threads
60
Messages
2,771
Reaction score
5,816
Location
Bay Area
Vehicles
2023 KIA EV6 GT, 20214 Hyundai Ioniq 5 Ltd AWD
Occupation
former electric pony jockey, flatbed towing expert
Country flag
That sounds completely correct. I have a 50A circuit with my ChargePoint Home Flex set to charge at the max non-hardwired at 40A and I get 9.2kHw.
 

ARK

Well-Known Member
Joined
Aug 21, 2020
Threads
45
Messages
2,940
Reaction score
4,297
Location
Los Angeles
Vehicles
'21 Premium SR AWD
Country flag
Open the ChargePoint app, bring up the menu. Choose Home Charge then Settings. Next, choose Power Source (hardwired) and choose the Amperage (70 for you) and hit save.

Does this fix it?

EDIT: Just reread your post and thought you said it was charging around 12 amps. At a bit less than 12 kWh, that sounds like 48 amps when combined with 240v.
 


generaltso

Well-Known Member
Joined
Jun 24, 2020
Threads
76
Messages
15,389
Reaction score
28,696
Location
Vermont
Vehicles
2024 Kia EV9 GT-Line
Country flag
Open the ChargePoint app, bring up the menu. Choose Home Charge then Settings. Next, choose Power Source (hardwired) and choose the Amperage (70 for you) and hit save.

Does this fix it?
Fix what? Nothing is broken.
 

ShadowCVL

Well-Known Member
First Name
Chris
Joined
Jul 26, 2021
Threads
12
Messages
216
Reaction score
134
Location
40601
Vehicles
Jeep Grand Cherokee, GMC Sierra, MME Premium
Occupation
IT and Electronics
Country flag
Is this hardwired to a 70 amp breaker? How did you fit the #3 conductors into the connectors?

If you ran #6 you should be using a 50amp breaker.

Something doesnt add up. But the max size breaker for a hardwired chargepoint home flex is 60amp, so something is wrong here. if something happens and the chargepoint pulls too much amperage itll catch fire without the breaker tripping if the breaker is too big.
 
OP
OP
jdunc87

jdunc87

Well-Known Member
First Name
Josh
Joined
May 18, 2021
Threads
10
Messages
181
Reaction score
251
Location
Columbus, OH
Vehicles
21 Mach E GT PE, 20 Mustang GT 401A PP1, 21 F150
Occupation
make stuff go faster
Country flag
Is this hardwired to a 70 amp breaker? How did you fit the #3 conductors into the connectors?

If you ran #6 you should be using a 50amp breaker.

Something doesnt add up. But the max size breaker for a hardwired chargepoint home flex is 60amp, so something is wrong here. if something happens and the chargepoint pulls too much amperage itll catch fire without the breaker tripping if the breaker is too big.
You are correct. its a 60a breaker. I didnt realize yesterday when I posted this the error.
 

SnBGC

Well-Known Member
First Name
Greg
Joined
Apr 20, 2020
Threads
46
Messages
5,962
Reaction score
9,778
Location
Phoenix
Vehicles
2021 Mach-E FE, 2021 Wrangler 4xe High Altitude
Occupation
Manager
Country flag
Is this hardwired to a 70 amp breaker? How did you fit the #3 conductors into the connectors?

If you ran #6 you should be using a 50amp breaker.

Something doesnt add up. But the max size breaker for a hardwired chargepoint home flex is 60amp, so something is wrong here. if something happens and the chargepoint pulls too much amperage itll catch fire without the breaker tripping if the breaker is too big.
We use connector ends on #4 wire that fits into the #6 size landing points inside the unit when using a 70A breaker. This allows the unit to function at 50A output which is its highest setting.

The CP 80A unit has provisions for much larger wire. We are installing those at the Safelite locations around the valley. Or we will be.....as soon as they arrive. Haven't seen one in person yet though.
Sponsored

 
 







Top