I have ordered a Mach-E. I have a dedicated 240V 50A circuit in my garage. Currently, though, it has a L6-30R outlet. Would this adapter work with the Ford Mobile Charger? Thanks.
Ford Mustang Mach-E Will an outlet adapter work? canvas
Sponsored

 

RickMachE

Well-Known Member
Joined
Jul 1, 2021
Threads
267
Messages
17,926
Reaction score
27,918
Location
SE MI
Vehicles
2022 Mach-E Premium 4X, 2022 Lightning Lariat ER
Country flag
You do realize that the proper outlet would cost much less?
 

mkhuffman

Well-Known Member
First Name
Mike
Joined
Nov 19, 2020
Threads
29
Messages
6,875
Reaction score
9,507
Location
Virginia
Vehicles
2025 Rivian R1T Tri-Max, Jeep GC-L, VW Jetta
Country flag
I have ordered a Mach-E. I have a dedicated 240V 50A circuit in my garage. Currently, though, it has a L6-30R outlet. Would this adapter work with the Ford Mobile Charger? Thanks.
canvas.webp
No, because a L6-30R outlet is rated for 30 amps, not 50 amps. You should have a 30 amp circuit breaker on that outlet. If you don't, it is a fire hazard.

The Ford charger will attempt to draw 48 amps and will either damage your outlet or cause your breaker to throw.

Edit: the Ford charger draws 32 amps, not 48. Sorry about that. Still a problem though.
 

RickMachE

Well-Known Member
Joined
Jul 1, 2021
Threads
267
Messages
17,926
Reaction score
27,918
Location
SE MI
Vehicles
2022 Mach-E Premium 4X, 2022 Lightning Lariat ER
Country flag
The Ford Mobile charger will only pull 32 amps, but the outlet should be changed.
 
OP
OP

babychef

Member
First Name
Adrian
Joined
Feb 25, 2022
Threads
1
Messages
5
Reaction score
7
Location
USA
Vehicles
2021 Mazda CX-5; 2022 Mustang Mach-E (ordered)
No, because a L6-30R outlet is rated for 30 amps, not 50 amps. You should have a 30 amp circuit breaker on that outlet. If you don't, it is a fire hazard.

The Ford charger will attempt to draw 48 amps and will either damage your outlet or cause your breaker to throw.

Edit: the Ford charger draws 32 amps, not 48. Sorry about that. Still a problem though.
I understand, but there is actually a 50A breaker on that circuit.
 


OP
OP

babychef

Member
First Name
Adrian
Joined
Feb 25, 2022
Threads
1
Messages
5
Reaction score
7
Location
USA
Vehicles
2021 Mazda CX-5; 2022 Mustang Mach-E (ordered)
No, because a L6-30R outlet is rated for 30 amps, not 50 amps. You should have a 30 amp circuit breaker on that outlet. If you don't, it is a fire hazard.

The Ford charger will attempt to draw 48 amps and will either damage your outlet or cause your breaker to throw.

Edit: the Ford charger draws 32 amps, not 48. Sorry about that. Still a problem though.
I understand, but there is actually a 50A breaker on that circuit.
 
OP
OP

babychef

Member
First Name
Adrian
Joined
Feb 25, 2022
Threads
1
Messages
5
Reaction score
7
Location
USA
Vehicles
2021 Mazda CX-5; 2022 Mustang Mach-E (ordered)
You do realize that the proper outlet would cost much less?
A proper outlet would cost less than $24? Also, I already have a 240V outlet installed which I use intermittently for another purpose. I am just wondering if I can use this adapter for the Ford charger.
 

mkhuffman

Well-Known Member
First Name
Mike
Joined
Nov 19, 2020
Threads
29
Messages
6,875
Reaction score
9,507
Location
Virginia
Vehicles
2025 Rivian R1T Tri-Max, Jeep GC-L, VW Jetta
Country flag
I understand, but there is actually a 50A breaker on that circuit.
That is a fire hazard. The outlet is rated for 30 amps, so if you draw 32 amps it will exceed the rating of the outlet significantly and the breaker will not throw to prevent a fire. The breaker is supposed to be rated for the lowest current allowed on the circuit which is 30 amps.

What size wire do you have going to that outlet? If the wire is also rated for 30 amps you have an even bigger fire hazard.
 

SpaceEVDriver

Well-Known Member
Joined
Aug 26, 2021
Threads
71
Messages
2,651
Reaction score
4,774
Location
Arizona
Vehicles
2022 CA Route 1 AWD, ER; 2023 Lightning Lariat ER
Occupation
Planetary Science
Country flag
I understand, but there is actually a 50A breaker on that circuit.
This is a fire hazard. The breaker is not designed to protect your equipment, it's there to protect the wiring and the outlet. Your outlet is not capable of carrying 50A, but you try to pull 50A, it could catch fire before the breaker trips. Similarly, the wiring is likely not capable of carrying 50A.
 

KevinS

Well-Known Member
Joined
Oct 11, 2021
Threads
34
Messages
1,515
Reaction score
2,831
Location
Maryland
Vehicles
2021 Mach-E (sold), 2023 Ioniq 6 SEL
Country flag
Just my opinion, but doing the home charger the right way (properly sized, professionally installed and independently inspected) is a no-brainer. It's a $50k+ car. Why would you want to scrimp on such an important detail of ownership?
 

mkhuffman

Well-Known Member
First Name
Mike
Joined
Nov 19, 2020
Threads
29
Messages
6,875
Reaction score
9,507
Location
Virginia
Vehicles
2025 Rivian R1T Tri-Max, Jeep GC-L, VW Jetta
Country flag
If (and this is a big if considering the outlet is rated for 30 amps) the wire is properly sized for a 50 amp circuit, then you can replace the outlet with a 50 amp outlet and then get an adapter for your 30 amp use case. That is safe.

If the wire is not rated for 50 amps and is instead rated for 30 amps, you absolutely should not put a 50 amp outlet on the circuit and you should definitely replace that circuit breaker with a 30 amp one. Until you do that, you have a fire hazard.

This is serious stuff and National Electrical Code (NEC) standards should not be ignored.
 

Nklem

Well-Known Member
First Name
Norm
Joined
May 20, 2021
Threads
105
Messages
1,318
Reaction score
1,699
Location
Coast of Maine
Vehicles
Subaru Solterra
Occupation
Mechanical Engineer
Country flag
The Ford Mobile charger will only pull 32 amps, but the outlet should be changed.
It only pulls 28 amps but still not code compliant To do that on a 30Amp circuit.
 

mkhuffman

Well-Known Member
First Name
Mike
Joined
Nov 19, 2020
Threads
29
Messages
6,875
Reaction score
9,507
Location
Virginia
Vehicles
2025 Rivian R1T Tri-Max, Jeep GC-L, VW Jetta
Country flag

Murse-In-Airy

Well-Known Member
First Name
Rod
Joined
Mar 5, 2021
Threads
82
Messages
3,678
Reaction score
8,297
Location
Chaumont, NY
Vehicles
Mach-E ER AWD
Occupation
Nurse
Country flag
My 2¢, and while I’m not an electrician I’ve done quite a bit of wiring.
A NEMA 14-50 outlet at Lowe’s is $10.
See here
If the wiring is appropriate for the 50 amp breaker, then this solves the fire hazard problem and you can plug in your EVSE safely.

Then, buy an adapter L6-30R, so you can still use whatever you are currently plugging in sometimes.
See here

Adapting down will pull less power through the appropriately sized 14-50 outlet.

If you really really don’t want to change the outlet, and you want to use the adapter, you should get a different EVSE that you can set to pull no more than 24 amps which will keep that 30 amp plug from heating up. Full disclosure, that is what I did. I bought a Grizzl-E classic and set it to 24 amps then used an adapter just like you’re showing on my 240 V 30 amp outlet I already had for my air compressor. But that was a holdover until I could get a proper 50 amp outlet installed. Then I just set the grizzl-e for 40 amps.