I am sure this has been hammered to death in the forums but my searches aren't finding much of supportive information onit.

So I purchased the Chargepoint Home Flex Level 2 48 amp charger. The charger is designed to use only 80% of whatever amp breaker you tell it that you put in. So for me to get the full 48 amps of charging in theory I would need a 60 amp breaker.

Now with that said I know a 6/3 is only rated at 55 amps and if I was actually pulling 60 amps that it would not work, but with me only pulling 48 amps or 50 amps max if I switch chargers down the road is it ok to use 6/3 with a 60 amp breaker but only using 50 or less amps?

Thanks,
AH
Sponsored

 

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
34
Messages
5,698
Reaction score
8,087
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
6/3 MC or SER is good for 60+. Just not NM (no, you can’t use it and meet code).
The branch circuit for an EVSE must be sized at a minimum of 125% rated current. That’s why you need a 60A circuit for a 48A EVSE.

Another option is to use a 50A breaker and commission the ChargePoint for 40A.
 

flapjake314

Well-Known Member
Joined
Jan 8, 2022
Threads
38
Messages
682
Reaction score
747
Location
NYC
Vehicles
Mach-E Select AWD
Country flag
Another option is to use a 50A breaker and commission the ChargePoint for 40A.
yeah i came here to say this, i don't own the chargepoint but i think virtually all these chargers can be down-rated and may even do so automatically... if you're somehow not able to do a 60A breaker you're not forced to, you'll just charge at a lower speed
 
OP
OP

Ndgame

Member
First Name
Aaron Hamm
Joined
Apr 11, 2024
Threads
3
Messages
8
Reaction score
1
Location
43015
Vehicles
2022 Mach-E GTPE
Country flag
Thanks everyone. So I have 1 more question. When I look at 6/3 MC cable it is showing 4 wires (black,red,white, and green) however when I look at 6/2 MC able it is 3 cables (black,white, and green). So it apprears that the 6/2 3 wire MC is what I want correct?
 

voerman

Well-Known Member
First Name
Lou
Joined
Aug 30, 2022
Threads
0
Messages
47
Reaction score
59
Location
NC
Vehicles
2023 Space White Premium AWD ER MME
Occupation
Retired
Country flag
Thanks everyone. So I have 1 more question. When I look at 6/3 MC cable it is showing 4 wires (black,red,white, and green) however when I look at 6/2 MC able it is 3 cables (black,white, and green). So it apprears that the 6/2 3 wire MC is what I want correct?
I assume you will get many answers but here goes:

The charger when hard wired (at least all the ones I have heard of) only need three wires, 2 hot and one ground. The white wire in the 6/3 cable is for a neutral which your charger does not use. When you wire the charger (with 6/2) be sure to tape over the white wire with black or red tape both in the panel box and in the charger. This tells anyone who might look that the white wire is being used as a hot wire and is not a neutral. The black wire is the other hot and the green one is ground. This is standard practice for wiring chargers and other appliances which are hard wired and do not require a neutral.

Of course, the two hot wires need to be connected to the two poles on your 240 volt breaker. Be sure to connect the ground wire to the ground bus, not the neutral bus if they are separate in your panel box (they may or may not be depending on whether it is a main or subpanel).

Hope that was not too confusing.
Lou
 


Mach-Lee

Well-Known Member
First Name
Lee
Joined
Jul 16, 2021
Threads
262
Messages
11,382
Reaction score
25,070
Location
Wisconsin
Vehicles
2022 Mach-E Premium AWD
Occupation
Sci/Eng
Country flag
Thanks everyone. So I have 1 more question. When I look at 6/3 MC cable it is showing 4 wires (black,red,white, and green) however when I look at 6/2 MC able it is 3 cables (black,white, and green). So it apprears that the 6/2 3 wire MC is what I want correct?
You only need 6/2 for the charger. 6/3 is a waste.
 

House MD

Well-Known Member
First Name
Alex
Joined
Mar 23, 2024
Threads
1
Messages
51
Reaction score
31
Location
Oregon
Vehicles
Mach E Premium
Occupation
Operation
Country flag
I installed ChargePoint with 60a breaker, 6awg THHN, and I'm running it at 48a.

Do not use Romex/NM for the charger, they are only rated for 55amps.
 

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
34
Messages
5,698
Reaction score
8,087
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
yeah i came here to say this, i don't own the chargepoint but i think virtually all these chargers can be down-rated and may even do so automatically... if you're somehow not able to do a 60A breaker you're not forced to, you'll just charge at a lower speed
They cannot detect the breaker size. Some have a physical switch that must be set, some ask you the breaker size during setup in the app. The second case is as close to automatic as it gets.
 

flapjake314

Well-Known Member
Joined
Jan 8, 2022
Threads
38
Messages
682
Reaction score
747
Location
NYC
Vehicles
Mach-E Select AWD
Country flag
They cannot detect the breaker size. Some have a physical switch that must be set, some ask you the breaker size during setup in the app. The second case is as close to automatic as it gets.
i have the tesla one and it detects on its own. maybe you have specific knowledge of OP's chargepoint unit though
 

Mach-Lee

Well-Known Member
First Name
Lee
Joined
Jul 16, 2021
Threads
262
Messages
11,382
Reaction score
25,070
Location
Wisconsin
Vehicles
2022 Mach-E Premium AWD
Occupation
Sci/Eng
Country flag
i have the tesla one and it detects on its own. maybe you have specific knowledge of OP's chargepoint unit though
No, the Tesla ones don't either. It has to be set in the WiFi portal during setup. It's impossible to auto-detect breaker size, a human has to enter it at some point.
 

RickMachE

Well-Known Member
Joined
Jul 1, 2021
Threads
267
Messages
17,957
Reaction score
27,994
Location
SE MI
Vehicles
2022 Mach-E Premium 4X, 2022 Lightning Lariat ER
Country flag
I had my electrician wire the circuit with 4 conductor wire, even though we were hardwiring and only needed 3. That way, if a 14-50 outlet is ever desired in the future, everything is ready for it.
 

Hammered

Banned
Banned
Joined
Oct 4, 2022
Threads
26
Messages
1,303
Reaction score
1,175
Location
SE US
Vehicles
2022 PB F150, MME GTPE
Country flag
i have the tesla one and it detects on its own. maybe you have specific knowledge of OP's chargepoint unit though
Yeah, not how it works. Tesla has some very poor wording in their manual and some foolishly believe it's "automatic". They really need to correct that. That's referring to if there's multiple EVSEs, each on their own circuit breaker, you can tell them the MAX power that can be pulled from all of them. Say if there's 3x 48a EVSEs, they can be told to never pull more than 100 amps and that 100 amp bucket will be shared between all 3 units ala "automatic load management".

Ford Mustang Mach-E Breaker for new Garage charger. 1713389906445-gy

Ford Mustang Mach-E Breaker for new Garage charger. 1713390067922-4u
 

Fremont Kid

Well-Known Member
First Name
Steve
Joined
Oct 8, 2022
Threads
12
Messages
773
Reaction score
667
Location
Colorado Springs, CO
Vehicles
2022 Mustang Mach e Premium AWD
Occupation
Retired IT
Country flag
Cost compared to 3 wire vs 4 wire is fairly minimal considering 4 wire cable will future proof your setup. I have 4 wire AWG6 both for my Mach-e charger and for a new induction cooktop/oven. 50A circuits for both.
 

flapjake314

Well-Known Member
Joined
Jan 8, 2022
Threads
38
Messages
682
Reaction score
747
Location
NYC
Vehicles
Mach-E Select AWD
Country flag
Yeah, not how it works. Tesla has some very poor wording in their manual and some foolishly believe it's "automatic". They really need to correct that. That's referring to if there's multiple EVSEs, each on their own circuit breaker, you can tell them the MAX power that can be pulled from all of them. Say if there's 3x 48a EVSEs, they can be told to never pull more than 100 amps and that 100 amp bucket will be shared between all 3 units ala "automatic load management".
i own and commissioned the tesla charger. i have 50A breakers even though the charger is capable of using 60A breakers. when i turned it on for the first time it automatically selected 50A.

i even purposely TRIED to switch it to 60A (long story, but i was trying to test whether anyone could mess it up) and the answer is no, the charger did not let me select 60A.
 

shelnian

Well-Known Member
First Name
Ian
Joined
Apr 25, 2022
Threads
1
Messages
407
Reaction score
295
Location
Seattle
Vehicles
2022 MME Premium AWD, 2023 Lightning XLT SR 312A
Occupation
Retired
Country flag
It meets code to use 6/3 connected to a 60A breaker. Hardwired 6/3 doesn't require a GFCI breaker like a 14-50 would.