Love that smart people like you are pioneering, but that procedure is beyond my technical skillset or comfort level. I’m optimistic this will be packed in a more consumer friendly way in the next generation of EVs.you are VERY close to having emergency backup.....
Grid-tied PV won't help you in Grid outage unless you have a hybrid inverter and built in transfer switch and batteries. But, with your EV you have all the battery you need!
As long as you are willing and able to follow simple procedures to isolate your house from the grid before using your EV as an Emergency Generator; you do not NEED an automatic transfer switch. All you really need is a little (1500watt) pure-sine Inverter for $300 or less, which you can energize via Jumper cables to your 12v connection points.
Then you can run extension cords to direct loads, OR you can fabricate male-male plug adaptors and 'backfeed' the nearest regular 15 amp outlet AFTER isolating from the grid and turning OFF your Solar circuit. If you backfeed one outlet on each 'leg' of your service panel, you effectively have 'whole house' backup.... but you MUST turn off main breaker, all 240 load breakers, Solar backfeed breaker, and all non-critical 120v loads to keep the maximum load well below 1500 watts if you are extracting energy from your MME.
*** Manual isolation, and use of male-male adapters with any Emergency Generator is NOT fool proof, and presents shock hazard if procedure is not followed. ***