Again the issue is the access cover on the backside of the conduit body would not be accessible inside the finished wall. That would fail inspection. I don’t think conduit will work for a rear entry if you need to pass inspection.Thank you, using 6” walls so hopefully can make the 90 turn with the right conduit box.
So will have a 1” conduit hole in wall with 2/6 coming out.
MC is the best option since it will allow #6 wire instead of #4 Romex. With 6” studs, I think the bend works, but I haven’t checked.Yes, you can drill the hole in the back.
If you want flush use romex and just have it stub out of the wall. Use a cable clamp in the conduit hole. The EVSE will act as the junction box. 40A setting with romex.
Can’t make the 90° bend in the wall legally with conduit and have it accessible. MC cable might be another option if you can bend it sharp enough in the wall.
MC is the best option since it will allow #6 wire instead of #4 Romex. With 6” studs, I think the bend works, but I haven’t checked.
Another option is to run smaller wire
Thinking I have two options:Again the issue is the access cover on the backside of the conduit body would not be accessible inside the finished wall. That would fail inspection. I don’t think conduit will work for a rear entry if you need to pass inspection.
I asked the same question a year and a half ago. This thread has the best info. Post 373. I popped the beauty cover off of mine and the mountain bracket measures approximately 8-1/2” W x 7” H. I can’t get to the opening to measure it.Thinking I have two options:
A) called building inspector this morning and I can leave the wire loose. Ready to put in back of charger. As long as the other side of the wire is NOT hooked up to the 220 box.
B) does anyone know the dimensions of the inside of the mounting bracket? I can use a box a little smaller than this, then put a cover over it for now.
I'm installing my charger later this week. I'm going to run 6/3 UFB, and will run it from my box around the corner of the house and straight into where I'll mount the charger in the garage. I was thinking about putting 18-24 deep, do I need to run conduit or just where it goes underground? I'm confused on that whole part....would it just be 1 inch PVC or what would I use to bring it underground then back up and into the garage? would this be what I'd use to make the 90 degree angle to bring it in? https://www.menards.com/main/electr...onduit-body/e986gr/p-1444444970422-c-9538.htm any guidance is appreciated, I've got the ditch digging part down as well as the electrical connections (60 amp breaker to run at 48)