Hardwiring EVSE vs plug-in option

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
34
Messages
5,687
Reaction score
8,068
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
It’s mostly the wire. That’s thick gauge wire that needs to be run for the 60A. The 50A wire is no slouch either, but you’re more likely to already have that run. (For example, I had a 50A outlet for an electric stove run across the basement from the breaker box to the kitchen/garage wall. I just pulled that out of the kitchen and rerouted it through the garage wall to install a 14-50 outlet. If I wanted to hardwire on 60A, an electrician would have to come out, run probably thousands of dollars in cable, and then wire it up.)
If the circuit is run in conduit, the wire size is the same for 50 vs 60A. Only NM cable would require larger wire for 60A.
Sponsored

 

JohnnyForensic

Well-Known Member
First Name
John
Joined
Apr 14, 2021
Threads
44
Messages
1,208
Reaction score
2,191
Location
VA, US
Vehicles
'21 Infinite Blue MME 4X Premium
Occupation
Digital Forensics
Country flag
If the circuit is run in conduit, the wire size is the same for 50 vs 60A. Only NM cable would require larger wire for 60A.
Conduit? That’s like…a professional job! :)
 

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
34
Messages
5,687
Reaction score
8,068
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
Conduit? That’s like…a professional job! :)
I’ve seen some PVC conduit runs that were definitely not done professionally. ?
A real giveaway is when it’s run outdoors without expansion joints. On really hot days, it sags like a wet noodle!
 

phidauex

Well-Known Member
First Name
Sam
Joined
Dec 8, 2020
Threads
17
Messages
966
Reaction score
1,843
Location
Colorado
Vehicles
2021 MachE 4EX, 2006 Prius, 1997 Tacoma
Occupation
Renewable Energy Engineer
Country flag
One “hybrid” option is to run MC (Metal Clad) cable. It is THWN cable pre assembled in a metallic jacket. It can get the better ampacity rating, but doesn’t require you to mount and pull conduit, you can just attach as you go. It also has the benefit of being able to be surface mounted, rather than NM/Romex which has to be in the wall or otherwise protected.

It takes a little practice to pull MC tight so that the runs look clean (not “floppy”) but it is nice to work with. Very popular in industrial environments for that reason.
 

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
34
Messages
5,687
Reaction score
8,068
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
One “hybrid” option is to run MC (Metal Clad) cable. It is THWN cable pre assembled in a metallic jacket. It can get the better ampacity rating, but doesn’t require you to mount and pull conduit, you can just attach as you go. It also has the benefit of being able to be surface mounted, rather than NM/Romex which has to be in the wall or otherwise protected.

It takes a little practice to pull MC tight so that the runs look clean (not “floppy”) but it is nice to work with. Very popular in industrial environments for that reason.
And due to crazy supply chain issues, I’ve seen places where MC costs less than NM.