I check with a freebie multimeter from Harbor Freight.
wait, people pay for Harbor Freight multimeters? "freebie" seems redundant.
 

macchiaz-o

Well-Known Member
First Name
Jonathan
Joined
Nov 25, 2019
Threads
169
Messages
8,176
Reaction score
15,338
Location
🔑 ]not/A/gr8'Place.2.store-mEyePassword[ 👀
Vehicles
MY21 J1 Premium RWD SR
Country flag
wait, people pay for Harbor Freight multimeters? "freebie" seems redundant.
Just to follow up... Sure enough, the leads that came with the FREE* multimeter are long enough to check a 14-50R's continuity and voltage. Worked great.

* with $1+ purchase
 


Sweetwater

Well-Known Member
Joined
Feb 5, 2020
Threads
14
Messages
500
Reaction score
345
Location
Ohio
Vehicles
Jeep
Occupation
Retired Electrician
Country flag
No one has addressed the NEC for providing a disconnect for your
240 V recp in your garage. It is required and I will install a disconnect.

Article :
625.2342 Disconnecting Means.
For electric vehicle supply equipment rated more than 60 amperes or more than 150 volts to ground, the disconnecting means shall be provided and installed in a readily accessible location. The disconnecting means shall be capable of being locked in the open position. The provision for locking or adding a lock to the disconnecting means shall be installed on or at the switch or circuit breaker used as the disconnecting means and shall remain in place with or without the lock installed. Portable means for adding a lock to the switch or circuit breaker shall not be permitted.
 

RonTCat

Well-Known Member
First Name
Ron
Joined
Jul 21, 2020
Threads
27
Messages
1,110
Reaction score
2,927
Location
USA
Vehicles
Mach-E wannabuy
Country flag
No one has addressed the NEC for providing a disconnect for your
240 V recp in your garage. It is required and I will install a disconnect.

Article :
625.2342 Disconnecting Means.
For electric vehicle supply equipment rated more than 60 amperes or more than 150 volts to ground, the disconnecting means shall be provided and installed in a readily accessible location. The disconnecting means shall be capable of being locked in the open position. The provision for locking or adding a lock to the disconnecting means shall be installed on or at the switch or circuit breaker used as the disconnecting means and shall remain in place with or without the lock installed. Portable means for adding a lock to the switch or circuit breaker shall not be permitted.
You would have to have a Level 3 charger to exceed these thresholds.
 

CHeil402

Well-Known Member
First Name
Chris
Joined
Sep 21, 2020
Threads
8
Messages
723
Reaction score
1,316
Location
King of Prussia, PA
Vehicles
2017 Audi A4, 2021 MME
Occupation
Electrical Engineer
Country flag
You would have to have a Level 3 charger to exceed these thresholds.
Agreed (in most cases)! Technically, SAE defines L2 as 240 V residential or 208 V commercial power to supply between 6 and 80 A. I haven't seen any residential L2 chargers greater than 60 A (and if you're using a NEMA 14-50 outlet, you're capped at 50 A) and most US residential service is split-phase, so line-to-ground voltage is only 120 V.

So two things to consider:
1. Are you hardwiring an EVSE that supplies more than 60 A (again if using a NEMA 14-50 outlet you're capped at 50 A)?
2. Are you using residential split-phase voltage? If yes, then your line-to-ground voltage is only 120 V.

If you're below 60 A and using US residential split-phase power (120 V line-to-ground), then you don't need a disconnect.
 

All Hat No Cattle

Well-Known Member
Joined
Oct 24, 2020
Threads
19
Messages
446
Reaction score
564
Location
Las Vegas
Vehicles
2023 Genesis GV-80 , 2017 Edge Titanium
Country flag
If you have your charger far from your circuit breaker, out of line-of-sight, a safety disconnect might be nice to have.

In my state we use these disconnects on 5-ton AC installations.

For $10, and a bit of wire, it is cheap insurance.

Disconnect
 

Sweetwater

Well-Known Member
Joined
Feb 5, 2020
Threads
14
Messages
500
Reaction score
345
Location
Ohio
Vehicles
Jeep
Occupation
Retired Electrician
Country flag
You would have to have a Level 3 charger to exceed these thresholds.
You need the disconnect. There are 2 requirements that states the use of a disconnect.
The one we all may have is :
"or more than 150 volts to ground"
The 120 V recp does not meet the requirements for a disconnect.
 

Sweetwater

Well-Known Member
Joined
Feb 5, 2020
Threads
14
Messages
500
Reaction score
345
Location
Ohio
Vehicles
Jeep
Occupation
Retired Electrician
Country flag
If you have your charger far from your circuit breaker, out of line-of-sight, a safety disconnect might be nice to have.

In my state we use these disconnects on 5-ton AC installations.

For $10, and a bit of wire, it is cheap insurance.

Disconnect
This disconnect will not meet NEC code. In the new code ALL conductors must
be disconnected. The 2 Hots and 1 neutral. This will need a 3 Phase Non fused
disconnect.
 

GoGoGadgetMachE

Well-Known Member
First Name
Michael
Joined
Jan 23, 2020
Threads
153
Messages
5,614
Reaction score
12,655
Location
Ohio
Vehicles
2021 Mach-E 1st Ed., 2022 Lightning Platinum
Occupation
Professional forum cheerleader and fanboy
Country flag
This disconnect will not meet NEC code. In the new code ALL conductors must
be disconnected. The 2 Hots and 1 neutral. This will need a 3 Phase Non fused
disconnect.
I realize I'm being dense but are you saying that a circuit breaker on a dedicated circuit is not sufficient in those cases?
 

Sweetwater

Well-Known Member
Joined
Feb 5, 2020
Threads
14
Messages
500
Reaction score
345
Location
Ohio
Vehicles
Jeep
Occupation
Retired Electrician
Country flag
I realize I'm being dense but are you saying that a circuit breaker on a dedicated circuit is not sufficient in those cases?
They are sufficient but they must be insight of equipment. Installed next
to charger in garage.
 

GoGoGadgetMachE

Well-Known Member
First Name
Michael
Joined
Jan 23, 2020
Threads
153
Messages
5,614
Reaction score
12,655
Location
Ohio
Vehicles
2021 Mach-E 1st Ed., 2022 Lightning Platinum
Occupation
Professional forum cheerleader and fanboy
Country flag
They are sufficient but they must be insight of equipment. Installed next
to charger in garage.
wow, so even like other side of garage is no good?

hmm. TIL
 
 