Things to consider when DIY installing a wall charger / outlet
GoGoGadgetMachE
I check with a freebie multimeter from Harbor Freight.
wait, people pay for Harbor Freight multimeters? "freebie" seems redundant.
Just to follow up... Sure enough, the leads that came with the FREE* multimeter are long enough to check a 14-50R's continuity and voltage. Worked great.
* with $1+ purchase
Sweetwater
Jeep
Retired Electrician
No one has addressed the NEC for providing a disconnect for your
240 V recp in your garage. It is required and I will install a disconnect.
Article :
625.2342 Disconnecting Means.
For electric vehicle supply equipment rated more than 60 amperes or more than 150 volts to ground, the disconnecting means shall be provided and installed in a readily accessible location. The disconnecting means shall be capable of being locked in the open position. The provision for locking or adding a lock to the disconnecting means shall be installed on or at the switch or circuit breaker used as the disconnecting means and shall remain in place with or without the lock installed. Portable means for adding a lock to the switch or circuit breaker shall not be permitted.
RonTCat
Ron
Mach-E wannabuy
Article :
You would have to have a Level 3 charger to exceed these thresholds.
CHeil402
King of Prussia, PA
2017 Audi A4, 2021 MME
Electrical Engineer
Agreed (in most cases)! Technically, SAE defines L2 as 240 V residential or 208 V commercial power to supply between 6 and 80 A. I haven't seen any residential L2 chargers greater than 60 A (and if you're using a NEMA 14-50 outlet, you're capped at 50 A) and most US residential service is split-phase, so line-to-ground voltage is only 120 V.
So two things to consider:
1. Are you hardwiring an EVSE that supplies more than 60 A (again if using a NEMA 14-50 outlet you're capped at 50 A)?
2. Are you using residential split-phase voltage? If yes, then your line-to-ground voltage is only 120 V.
If you're below 60 A and using US residential split-phase power (120 V line-to-ground), then you don't need a disconnect.
All Hat No Cattle
Las Vegas
2023 Genesis GV-80 , 2017 Edge Titanium
If you have your charger far from your circuit breaker, out of line-of-sight, a safety disconnect might be nice to have.
In my state we use these disconnects on 5-ton AC installations.
For $10, and a bit of wire, it is cheap insurance.
Disconnect
Sweetwater
Jeep
Retired Electrician
You need the disconnect. There are 2 requirements that states the use of a disconnect.
The one we all may have is :
"or more than 150 volts to ground"
The 120 V recp does not meet the requirements for a disconnect.
Sweetwater
Jeep
Retired Electrician
Disconnect
This disconnect will not meet NEC code. In the new code ALL conductors must
be disconnected. The 2 Hots and 1 neutral. This will need a 3 Phase Non fused
disconnect.
GoGoGadgetMachE
disconnect.
I realize I'm being dense but are you saying that a circuit breaker on a dedicated circuit is not sufficient in those cases?
Sweetwater
Jeep
Retired Electrician
They are sufficient but they must be insight of equipment. Installed next
to charger in garage.
GoGoGadgetMachE
wow, so even like other side of garage is no good?
hmm. TIL