I just upgraded my NEMA 14-50 outlet to a hardwire install. I didn't trust the outlet the electricians had used for my outlet, even though it currently looks fine. They used 4/3 aluminum SER to terminate into the outlet, so I got some 6/2 MC cable to pigtail from the junction box into the charger. I used a couple of Polaris IT-4B terminals to connect the aluminum cable to the copper cable that goes into the Chargepoint. I terminated the SER neutral with a wire nut and electrical tape.
My charger has a dedicated power meter for better TOD rates so I get a pretty accurate readout on what the system is pulling. Chargepoint would report on the 14-40 I was charging at 9.5kW, which means at 240V 40A I was losing about 100 watts to voltage drop. Now with the hardwire I'm seeing 11.4kW at the meter and 11.2kW reported from Chargepoint. That's double the amount of power lost to voltage drop across the power cabling vs when I was using the 14-50 outlet. I checked the voltage at the breaker and the terminal block inside the Chargepoint. It was ~241V and ~237V, so at 48A that's about the 200 watts of loss I'm seeing. Reducing to 40A to match what i got with the outlet I see similar losses, so more than I had before. I also measured the voltage across the Polaris connectors and it was identical to the 237V at the terminal block so I think those connections are good. Everything inside the junction box was slightly warm but nothing felt hot to the touch after about 30 minutes of charging. The Polaris connectors and breaker are all torqued to the manufacturer spec
This install goes from the outside of my house to a detached garage, the cable run is probably about 60 ft. Measuring the voltage shows a 1.7% voltage drop across the run from the breaker to the EVSE terminal block. Any ideas why I could be seeing more power loss across the cable vs what I had with the outlet and is this amount of voltage drop/power loss of any concern?
My charger has a dedicated power meter for better TOD rates so I get a pretty accurate readout on what the system is pulling. Chargepoint would report on the 14-40 I was charging at 9.5kW, which means at 240V 40A I was losing about 100 watts to voltage drop. Now with the hardwire I'm seeing 11.4kW at the meter and 11.2kW reported from Chargepoint. That's double the amount of power lost to voltage drop across the power cabling vs when I was using the 14-50 outlet. I checked the voltage at the breaker and the terminal block inside the Chargepoint. It was ~241V and ~237V, so at 48A that's about the 200 watts of loss I'm seeing. Reducing to 40A to match what i got with the outlet I see similar losses, so more than I had before. I also measured the voltage across the Polaris connectors and it was identical to the 237V at the terminal block so I think those connections are good. Everything inside the junction box was slightly warm but nothing felt hot to the touch after about 30 minutes of charging. The Polaris connectors and breaker are all torqued to the manufacturer spec
This install goes from the outside of my house to a detached garage, the cable run is probably about 60 ft. Measuring the voltage shows a 1.7% voltage drop across the run from the breaker to the EVSE terminal block. Any ideas why I could be seeing more power loss across the cable vs what I had with the outlet and is this amount of voltage drop/power loss of any concern?