I got a quote from an electrician about the work that needs to be done to get my charger installed (once I figure out which one I am getting!). I don’t know much about electrical work and am wondering if people could comment on whether the price sounds reasonable.

The electrician said I have a 200amp main panel (or service to the house, not sure on terminology here), but that the existing subpanel could not take an electric car charger on it. He said therefore he should install a 50amp subpanel and pull the line about five feet to where I want it outside of my garage and install a NEMA 14-50 outlet. The house’s main panel (am I using the right terminology here, the round meter outside the house where the electrical service comes in) and the main breaker box are both very close to the corner of the garage where I want my outdoor charger, so he only has like five feet of new wiring to run.

He said he would do all this for $500 parts and labor, exclusive of the EVSE that I buy and want him to install. I am in the Los Angeles area where our prices for this kind of thing tend to be higher. Is his price reasonable, very good, too high?

Not sure if this has been discussed anywhere in detail, if so my apologies, I’ve really only seen the group of threads on charger types or how to install the EVSE yourself. But I think a standalone thread for this could be valuable because I’d guess a new subpanel installation going to a new NEMA 14-50 outlet is probably among the more common types of electrical work people will need to get their EVSE installed.

EDIT: I know some of the beefier chargers, like Ford’s, would need a 60 amp panel as they draw up to 48amps. I am looking at the slower 32amp L2 chargers based on my needs. The electrician said if I want a 60amp subpanel vs a 50amp subpanel, there will be a material increase in price as he said the panel and wiring would have to be different.
That's a solid price. The electrician wanted $3500 to run 70ft of 6g cable from my panel in front of the house through the attic to my detached garage. I had some quotes as high as $5k!
Sponsored

 

FPLiptak

Well-Known Member
First Name
Frank
Joined
Jun 21, 2020
Threads
16
Messages
355
Reaction score
345
Location
Saint George, UT
Vehicles
Mach-E Premium ER AWD
Occupation
Retired
Country flag
I have no idea about the cost but what surprises me is the need for a sub-panel. I have 200 amp service and have had TWO 50 amp circuits in the garage for EVs and did not need a sub panel. This was new construction and there were no issues with getting a CO (Certificate of Occupancy) when the house was completed (2017)
 
  • Like
Reactions: ARK
OP
OP
ARK

ARK

Well-Known Member
Joined
Aug 21, 2020
Threads
45
Messages
2,938
Reaction score
4,297
Location
Los Angeles
Vehicles
'21 Premium SR AWD
Country flag
I agree if it was just an outlet. Adding a 60 amp sub-panel may be a different story.
Thank you, I will find out. He didn’t mention a permit, but I wouldn’t be surprised if he didn’t intend to pull one even if required...
 
OP
OP
ARK

ARK

Well-Known Member
Joined
Aug 21, 2020
Threads
45
Messages
2,938
Reaction score
4,297
Location
Los Angeles
Vehicles
'21 Premium SR AWD
Country flag
I have no idea about the cost but what surprises me is the need for a sub-panel. I have 200 amp service and have had TWO 50 amp circuits in the garage for EVs and did not need a sub panel. This was new construction and there were no issues with getting a CO (Certificate of Occupancy) when the house was completed (2017)
I may be wrong on the terminology. He looked at my electrical service outside (the round meter), said it was 200amps and therefore no problem, then looked at my breaker box in my garage and said he needed to add (here is where I could of sworn he said subpanel) because my existing hardware couldn’t accommodate an EVSE on it.
 

engnrng

Well-Known Member
First Name
Bruce
Joined
Feb 8, 2020
Threads
9
Messages
579
Reaction score
826
Location
SoCal
Vehicles
2022 GTPE, Kona EV, 2023 BMW iX
Occupation
Engineer
Country flag
I think a permit for a new outlet is something of a unicorn in SoCal.
Not sure what you mean by this. 3 years ago I had an electrician install a hard wired EVSE that was provided by my utility. Permit was quick, easy, and about $50 to $75 as I recall in Ventura County. All they needed was the specs (rated amps at 240V) on the EVSE. I handled it during an OTC (over the counter) visit, pre-COVID of course. Since I have homeowner's insurance, everything I do I get a permit, including replacing a water heater. Be aware, insurance claims can be challenged if you do NOT get the proper permits. A simple exterior 110V outdoor outlet permit here is $25. Not a big deal at all.
 


engnrng

Well-Known Member
First Name
Bruce
Joined
Feb 8, 2020
Threads
9
Messages
579
Reaction score
826
Location
SoCal
Vehicles
2022 GTPE, Kona EV, 2023 BMW iX
Occupation
Engineer
Country flag
I have no idea about the cost but what surprises me is the need for a sub-panel. I have 200 amp service and have had TWO 50 amp circuits in the garage for EVs and did not need a sub panel. This was new construction and there were no issues with getting a CO (Certificate of Occupancy) when the house was completed (2017)
Codes are not the same - my codes in the County are different from the codes required by a nearby city. In my case, a subpanel/disconnect box (about 6 inch by 10 inch) was required between my main panel and the EVSE. Some subpanel requirements are based on how much room there is left in the main panel.
 

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
34
Messages
5,688
Reaction score
8,068
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
I have no idea about the cost but what surprises me is the need for a sub-panel. I have 200 amp service and have had TWO 50 amp circuits in the garage for EVs and did not need a sub panel. This was new construction and there were no issues with getting a CO (Certificate of Occupancy) when the house was completed (2017)
Most likely, a subpanel isn't a need, but may still be a good idea. It provides lower-cost future flexibility (at a slightly higher initial cost) and in the unlikely event you do trip a breaker (or just need to power down the EVSE outlet) the breaker is right there in the garage instead of in your basement.
 
  • Like
Reactions: ARK

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
34
Messages
5,688
Reaction score
8,068
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
Codes are not the same - my codes in the County are different from the codes required by a nearby city. In my case, a subpanel/disconnect box (about 6 inch by 10 inch) was required between my main panel and the EVSE. Some subpanel requirements are based on how much room there is left in the main panel.
Good points - a disconnect is required either in sight or lockable. A subpanel is an easy way to meet this requirement.
 

bruceski88

Well-Known Member
First Name
Bruce
Joined
Aug 12, 2020
Threads
6
Messages
279
Reaction score
321
Location
CA
Vehicles
Mach e
Occupation
Retired Engineer
Country flag
I got a quote from an electrician about the work that needs to be done to get my charger installed (once I figure out which one I am getting!). I don’t know much about electrical work and am wondering if people could comment on whether the price sounds reasonable.

The electrician said I have a 200amp main panel (or service to the house, not sure on terminology here), but that the existing subpanel could not take an electric car charger on it. He said therefore he should install a 50amp subpanel and pull the line about five feet to where I want it outside of my garage and install a NEMA 14-50 outlet. The house’s main panel (am I using the right terminology here, the round meter outside the house where the electrical service comes in) and the main breaker box are both very close to the corner of the garage where I want my outdoor charger, so he only has like five feet of new wiring to run.

He said he would do all this for $500 parts and labor, exclusive of the EVSE that I buy and want him to install. I am in the Los Angeles area where our prices for this kind of thing tend to be higher. Is his price reasonable, very good, too high?

Not sure if this has been discussed anywhere in detail, if so my apologies, I’ve really only seen the group of threads on charger types or how to install the EVSE yourself. But I think a standalone thread for this could be valuable because I’d guess a new subpanel installation going to a new NEMA 14-50 outlet is probably among the more common types of electrical work people will need to get their EVSE installed.

EDIT: I know some of the beefier chargers, like Ford’s, would need a 60 amp panel as they draw up to 48amps. I am looking at the slower 32amp L2 chargers based on my needs. The electrician said if I want a 60amp subpanel vs a 50amp subpanel, there will be a material increase in price as he said the panel and wiring would have to be different.
I installed one myself in Placer County and had one installed in Sunnyvale by an electrician. Permit in Placer was $180 and I spent less than $100 on materials since the 6-3 Romex was already there. most of the cost was a high quality 14-50 outlet. I needed a new Main Panel in Sunnyvale and 70’ of Romex to reach the dedicated outlet so the cost was much more than yours. Actually went with someone who was more expensive on the outlet as he was much cheaper on the new panel. I believe 6-3 Romex will support up to a 60Amp breaker and a 48 hardwired charger
 
  • Like
Reactions: ARK

DBC

Well-Known Member
First Name
Don
Joined
Oct 1, 2020
Threads
8
Messages
1,224
Reaction score
1,430
Location
San Diego
Vehicles
Volt ELR
Country flag
Not sure what you mean by this. 3 years ago I had an electrician install a hard wired EVSE that was provided by my utility. Permit was quick, easy, and about $50 to $75 as I recall in Ventura County.
I was specifically talking about an outlet. I have never seen a permit pulled for a new outlet, regardless of whether it was 120v or 240v. Ditto for a new light fixture. Have you? (Of course if part of a major project that would be different).

My point was that the electrician might/would want to pull a permit for a hardwired EVSE.
 
  • Like
Reactions: ARK

kgautam28

Well-Known Member
Joined
Oct 22, 2020
Threads
19
Messages
219
Reaction score
433
Location
98036
Vehicles
Eco boost 2016, 2021 Mach e FE, 2022 Mach E GT PE
Occupation
Software
Country flag
I was quoted $450 with all parts, wires, sockets and permit in Seattle.with Lowen electric.

My charger costed $699, with tax credit for installation and charger it should be free.

My local utility provider also has $500 rebate in charger
 

duneii

Well-Known Member
First Name
Siri
Joined
Dec 27, 2020
Threads
1
Messages
45
Reaction score
79
Location
Seattle, WA
Vehicles
Chrysler Pacifica Plug-in '18, Mach E LR AWD-order
Country flag
Most likely, a subpanel isn't a need, but may still be a good idea.
Here’s a Pic of our panel which is 200A. You can see the "slim" breakers with the A/C and 50A socket. It avoided a subpanel.

I had both done at the same time and so don't know the separate costs. This was done 2 years ago when I go tired of the 110V charging on the Pacifica plug in... My weekday typical commute was around 28miles and so, 110V and Pacific's 32mile range was perfect.
Ford Mustang Mach-E Cost of Charger Installation by Electrician 20210131_112444
 

TheVirtualTim

Well-Known Member
First Name
Tim
Joined
Oct 11, 2020
Threads
26
Messages
1,366
Reaction score
2,469
Location
Dearborn, MI
Vehicles
‘21 Mach-E First Edition, ‘23 Mach-E GT Performance
Country flag
$500 is pretty reasonable and ... there's a federal tax credit for 30% of the install costs (save all your receipts for hardware and labor -- the tax credit is capped at $1000).

My wiring project was $6k (no kidding!) but it was MAJOR work. Oh... and we did a lot of the work ourselves and bought some of the equipment ourselves.

The problems that caused me to have a huge bill were that my home was built in 1940, I have a 100 amp meter socket and 100 amp service panel and I have a detached garage (which only has a single 20 amp 120 v circuit).

Basically ... if the project can be done without having to upgrade the existing meter or service panel and you have an attached garage (no long distance needed to run the wiring) then it's "cheap" (I consider a $500 to be a bargain price). If you have a detached garage or the service has to be upgraded ... it gets expensive!!
 

buffasnow

Well-Known Member
First Name
Jeff
Joined
Oct 20, 2020
Threads
2
Messages
436
Reaction score
782
Location
Buffalo, NY
Vehicles
Grabber Blue FE, 85 Mustang GT (pasturized)
Country flag
That's a solid price. The electrician wanted $3500 to run 70ft of 6g cable from my panel in front of the house through the attic to my detached garage. I had some quotes as high as $5k!
Holy cow. Sounds like they did not really want the work?

I got 100 ft of 4 ga metal clad run across basement, through garage wall, up through garage crawlspace and back down to new 14-50, EVSE install, including $75 permit and 50A breaker, for $900. Amazing the variation.
 

Maric

Well-Known Member
Joined
Jun 10, 2020
Threads
20
Messages
887
Reaction score
2,219
Location
NorCal
Vehicles
Grabber Blue FE
Occupation
Engineer
Country flag
Very reasonable bid honestly.