There is a prescribed way to determine load factors in the national electric code. You can’t just guess if you are doing it the right way, although the odds of an inspector actually checking may be low in many areas.I think you need to think at this from a different perspective. Are you using 77.1 amps continuously? I sincerely doubt it.
You don’t need to throw breakers on things that aren’t being used. Assuming you have an electric stove and dryer here. You probably just need to avoid using the dryer, stove, ac, and evse all at the same time. Even then, the stove and dryer aren’t pulling full power the whole time they are on. They cycle.
A 100A panel can easily be maxed out even in the real world if you add a 40A charger.