Can I install high quality 14-50 here?

Jtbuster

Well-Known Member
First Name
Brian oConnor
Joined
May 7, 2022
Threads
6
Messages
277
Reaction score
156
Location
Calif
Vehicles
Mach e
Country flag
QUOTE="Jtbuster, post: 753378, member: 12136"]
Quote:


“The code is very clear that you cannot install an evse that pulls 48 amps on 6-2. The issue is that that clarity requires looking at several different places in the code book and understanding the difference between maximum over current device and minimum circuit ampacity.





An EVSE is considered a continuous load.



NEC Article 100 defines continuous loads as loads that are expected to run continuously for 3hrs or more .



The minimum circuit ampacity (amount of current wire has to be rated for) is 125 percent of the continuous load, in this case 48*1.25= 60amps



NEC 210.19(A)(1) code reference for that.





Romex cable can only be used at the 60 degree c rating on the NEC ampacity tables.



NEC article 334.80 code reference for that.





Then, we need to look at the NEC ampacity tables. At 60c, #6 (6/2NM cable) is only rated for 55 amps. Commonly, people misapply the round up rule that allows you to round up the over current device (breaker) past the MOCP calculation to the next standard breaker size, which for 55 amps could be 60. However, we are calculating minimum circuit ampacity, not maximum over current protection, so the round up rule does not come to play.



So our options are to use 4/2NM which is rated at 70amps @ 60c (which is impossible to find) or to use #6thhn, which can be rated at 75c as long as the breaker and evse terminals are also rated at 75c (most are) which is rated at 65 amps.



NEC 310.16 reference for that.”
 

Space_Pony

Well-Known Member
Joined
Jun 7, 2023
Threads
4
Messages
1,699
Reaction score
1,436
Location
Indiana
Vehicles
2023 Premium Mach-E awdX
Country flag
QUOTE="Jtbuster, post: 753378, member: 12136"]
Quote:


“The code is very clear that you cannot install an evse that pulls 48 amps on 6-2. The issue is that that clarity requires looking at several different places in the code book and understanding the difference between maximum over current device and minimum circuit ampacity.





An EVSE is considered a continuous load.



NEC Article 100 defines continuous loads as loads that are expected to run continuously for 3hrs or more .



The minimum circuit ampacity (amount of current wire has to be rated for) is 125 percent of the continuous load, in this case 48*1.25= 60amps



NEC 210.19(A)(1) code reference for that.





Romex cable can only be used at the 60 degree c rating on the NEC ampacity tables.



NEC article 334.80 code reference for that.





Then, we need to look at the NEC ampacity tables. At 60c, #6 (6/2NM cable) is only rated for 55 amps. Commonly, people misapply the round up rule that allows you to round up the over current device (breaker) past the MOCP calculation to the next standard breaker size, which for 55 amps could be 60. However, we are calculating minimum circuit ampacity, not maximum over current protection, so the round up rule does not come to play.



So our options are to use 4/2NM which is rated at 70amps @ 60c (which is impossible to find) or to use #6thhn, which can be rated at 75c as long as the breaker and evse terminals are also rated at 75c (most are) which is rated at 65 amps.



NEC 310.16 reference for that.”
Don't use Romex. The temperature rating for THHN #6 wire is 90°C . THHN #6 wire can handle up to 75 amps.
 

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
34
Messages
5,687
Reaction score
8,068
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
QUOTE="Jtbuster, post: 753378, member: 12136"]
Quote:


“The code is very clear that you cannot install an evse that pulls 48 amps on 6-2. The issue is that that clarity requires looking at several different places in the code book and understanding the difference between maximum over current device and minimum circuit ampacity.





An EVSE is considered a continuous load.



NEC Article 100 defines continuous loads as loads that are expected to run continuously for 3hrs or more .



The minimum circuit ampacity (amount of current wire has to be rated for) is 125 percent of the continuous load, in this case 48*1.25= 60amps



NEC 210.19(A)(1) code reference for that.





Romex cable can only be used at the 60 degree c rating on the NEC ampacity tables.



NEC article 334.80 code reference for that.





Then, we need to look at the NEC ampacity tables. At 60c, #6 (6/2NM cable) is only rated for 55 amps. Commonly, people misapply the round up rule that allows you to round up the over current device (breaker) past the MOCP calculation to the next standard breaker size, which for 55 amps could be 60. However, we are calculating minimum circuit ampacity, not maximum over current protection, so the round up rule does not come to play.



So our options are to use 4/2NM which is rated at 70amps @ 60c (which is impossible to find) or to use #6thhn, which can be rated at 75c as long as the breaker and evse terminals are also rated at 75c (most are) which is rated at 65 amps.



NEC 310.16 reference for that.”
If you don’t want to tun conduit, #6 SER or MC cable is permitted for a 60A circuit.