Chargepoint Home Flex install (wired) - stripped wire prep?

grein002

Well-Known Member
First Name
Scott
Joined
Mar 5, 2024
Threads
9
Messages
266
Reaction score
409
Location
Durham, NC
Vehicles
2023 Mach-E GTPE, Red w/Gray interior
Country flag
I've purchased the ChargePoint Home Flex and mounted it to the wall. I have a 25' run of Wireco 8/3 THHN metal clad (see here) from the 60A breaker in my panel. If you are familiar with the charger, you will know that the included power cord has flattened metal "pins" to insert into the snap-close connectors. My question is, should I just insert the stripped 8AWG into these holes, or does it make sense to prep the stripped ends, perhaps by flattening and tinning with solder?
Sponsored

 

Mach-Lee

Well-Known Member
First Name
Lee
Joined
Jul 16, 2021
Threads
262
Messages
11,345
Reaction score
24,967
Location
Wisconsin
Vehicles
2022 Mach-E Premium AWD
Occupation
Sci/Eng
Country flag
First of all, #8 MC is only good for 50A with a 75°C termination temp. So you need to return the 60A breaker and get a 50A one. The EVSE will run at 40A. You also only need 8/2, neutral wire is not used.

Inserting copper wire strands into the ChargePoint terminals is acceptable.
 

ocdxfv

Well-Known Member
First Name
Matt
Joined
Feb 11, 2021
Threads
19
Messages
250
Reaction score
329
Location
Orange County, CA
Vehicles
2021 Mach E, 2013 Toyota Rav4 EV
Occupation
Retired radiology tech
Country flag
I wouldn’t solder them. I used a wire ferrule.
 

Maquis

Well-Known Member
First Name
Dave
Joined
Dec 21, 2020
Threads
34
Messages
5,688
Reaction score
8,068
Location
Illinois
Vehicles
2021 Mach E4X, 2023 Lightning Lariat ER
Country flag
I second what Mach-Lee said. If you needed to prep the wires in any special way for terminating, it would be spelled out in the installation instructions.
 

Stu H

Well-Known Member
First Name
Stu
Joined
Jan 14, 2022
Threads
5
Messages
46
Reaction score
21
Location
Vacaville
Vehicles
2021 Mach E GT Pe; 68 Corvette, others....
Occupation
Retired
Country flag
First of all, #8 MC is only good for 50A with a 75°C termination temp. So you need to return the 60A breaker and get a 50A one. The EVSE will run at 40A. You also only need 8/2, neutral wire is not used.

Inserting copper wire strands into the ChargePoint terminals is acceptable.
I thought that the following is a good rule (Copper wire):

15 Amp 14 ga
20 Amp 12 ga
30 Amp 10 ga
40 Amp 8 ga
50 Amp 6 ga
60 Amp 4 ga

1 size larger (lower ga number) if using aluminum wire....

Did I miss something?
 


Aubury

Well-Known Member
Joined
Dec 4, 2023
Threads
3
Messages
230
Reaction score
272
Location
Dearborn, MI
Vehicles
2023 Mach E Premium - Grabber Blue
Country flag
I thought that the following is a good rule (Copper wire):

15 Amp 14 ga
20 Amp 12 ga
30 Amp 10 ga
40 Amp 8 ga
50 Amp 6 ga
60 Amp 4 ga

1 size larger (lower ga number) if using aluminum wire....

Did I miss something?
You can't use aluminum directly in the chargepoint install. You would have to pigtail to copper before it goes into the EVSE.
 

david_quick

Well-Known Member
First Name
David
Joined
Sep 10, 2023
Threads
54
Messages
642
Reaction score
487
Location
Bremerton WA
Vehicles
2023 Mach E GT
Occupation
Retired
Country flag
First of all, #8 MC is only good for 50A with a 75°C termination temp. So you need to return the 60A breaker and get a 50A one. The EVSE will run at 40A. You also only need 8/2, neutral wire is not used.

Inserting copper wire strands into the ChargePoint terminals is acceptable.
this is one thing I noticed when I converted my EVSE from plug in to hard wired. The 14-50 it came with did not have a neutral. Now that has me wondering if they all are that way.
 
OP
OP

grein002

Well-Known Member
First Name
Scott
Joined
Mar 5, 2024
Threads
9
Messages
266
Reaction score
409
Location
Durham, NC
Vehicles
2023 Mach-E GTPE, Red w/Gray interior
Country flag
240V equipment doesn't need a neutral unless it needs 120V for some of its internal functions. If the EVSE doesn't need 120V, it has no internal connection for neutral, and they can save some $ by omitting the conductor / prong.
 

orangethunder

Well-Known Member
Joined
Nov 2, 2021
Threads
8
Messages
100
Reaction score
109
Location
California
Vehicles
On order
Country flag
I've purchased the ChargePoint Home Flex and mounted it to the wall. I have a 25' run of Wireco 8/3 THHN metal clad (see here) from the 60A breaker in my panel. If you are familiar with the charger, you will know that the included power cord has flattened metal "pins" to insert into the snap-close connectors. My question is, should I just insert the stripped 8AWG into these holes, or does it make sense to prep the stripped ends, perhaps by flattening and tinning with solder?
No need to flatten the wire. Just let the wire clamps do their thing.

But your breaker is too big for 8 gauge wire. Highly recommend you swap out with a 50amp breaker (which will charge at 40 amps, i.e. 80% of breaker size for use by continuous loads).
 
OP
OP

grein002

Well-Known Member
First Name
Scott
Joined
Mar 5, 2024
Threads
9
Messages
266
Reaction score
409
Location
Durham, NC
Vehicles
2023 Mach-E GTPE, Red w/Gray interior
Country flag
Yeah, I've ordered 6AWG MC to replace the 8AWG.
 

Mach-Lee

Well-Known Member
First Name
Lee
Joined
Jul 16, 2021
Threads
262
Messages
11,345
Reaction score
24,967
Location
Wisconsin
Vehicles
2022 Mach-E Premium AWD
Occupation
Sci/Eng
Country flag
Yeah, I've ordered 6AWG MC to replace the 8AWG.
Yes 6/2 is what you want for a hardwired 60A breaker. You have to look up the ampacity for the specific type of wire you’re using.