Why not just hit "OK"? Takes less time than off and on. And you can be moving.
Your math is wrong.

Breaker must be rated at 125% of rated load.

40 amp load x 1.25 = 50 amps.

If you divide 38 by 1.25 you get 24.
My math is fine. 38 or 40 either amount is safe. You need to multiply not divide, 38 x 1.25 is 47.5 and they don't make a 47.5 amp breaker so you go to the next size up which is 50. and #6 copper is rated at 55 amps so its a safe install if installed by a licensed electrician and inspected it will be right and I will be safe. Dont use cheap outlets. get a quality NEMA 14-50 outlet. You pay all this money for your EV so dont skimp on the products you need to charge it.
 
Last edited:

CherryBomb

Well-Known Member
First Name
Dave
Joined
Sep 8, 2022
Threads
5
Messages
109
Reaction score
143
Location
Ft Collins, Colorado
Vehicles
2022 Rapid Red Mach-e GT
Occupation
Retired
Country flag
Use a qualified electrician that will
Pull a permit
Install 6/6/6/3 NMB (Romex) with a 50 amp breaker (GFI per code)
Install an industrial grade NEMA 14-50 outlet
Charge at 38 amps
Get it inspected
Check torque once a year
=Safe Install with no worries.

All electrical installs that are continuous loads (running for 3 hours or more) must be rated at 125% of their rated load. So if you are planning to charge at 38 amps just divide 38 X 1.25 and it comes out to be 50 so a 50 amp breaker installed with #6 wire (which is rated at 55 amps @ 60°C ) and pulling only 38 amps will never have an issue if it's installed correctly. Just my 2 cents.
If you really want a safe applications, why use the NEMA outlet in the first place? Per the Munro Live episode, it is best to direct wire the to home EV equipment. I'm going to have the electrician do this when he installs my home equipment along with using THHN wire instead of Romex (higher temp rating and higher current rating). I would think this could end up saving you money on the install as well since you don't need the outlet nor the GFI breaker (although the wire is probably more expensive).
 

SnBGC

Well-Known Member
First Name
Greg
Joined
Apr 20, 2020
Threads
46
Messages
5,962
Reaction score
9,778
Location
Phoenix
Vehicles
2021 Mach-E FE, 2021 Wrangler 4xe High Altitude
Occupation
Manager
Country flag
I can’t say I’ve ever seen these; not that I’m a full time sparky.
Most all residential panels are press on. Most all commercial panels have bolt on breakers. Bolt down breakers are a much more positive method and superior to the press on type.
 


superdave80

Well-Known Member
First Name
David
Joined
Aug 18, 2022
Threads
5
Messages
1,332
Reaction score
2,027
Location
Santa Rosa, CA
Vehicles
2022 Mach E Select SR RWD
Country flag
If you really want a safe applications, why use the NEMA outlet in the first place? Per the Munro Live episode, it is best to direct wire the to home EV equipment.
How would one hardwire the portable charger that comes with the Mach E?
 

kindofblue

Well-Known Member
First Name
Reid
Joined
Dec 28, 2021
Threads
35
Messages
1,021
Reaction score
883
Location
Arroyo Grande CA
Vehicles
Grabber Blue Mach e Premium 11/5/22, '25 Lexus 45h+ PHEV
Occupation
Psychologist & developer of digital tools for alcohol misuse
Country flag
@Administrator Please make this a sticky thread. It's a topic that needs maximum exposure that persists on the forum. Thanks.
 

CherryBomb

Well-Known Member
First Name
Dave
Joined
Sep 8, 2022
Threads
5
Messages
109
Reaction score
143
Location
Ft Collins, Colorado
Vehicles
2022 Rapid Red Mach-e GT
Occupation
Retired
Country flag
How would one hardwire the portable charger that comes with the Mach E?
Yeah that's the rub ... This was mentioned in the episode as well. I believe it was suggested that we don't use the mobile charger on a daily basis as these NEMA outlets aren't made for repeated insertions even if you get a good one. They will wear out over time and become loose thereby becoming more dangerous. I plan on keeping mine in the car and using it only when I need it when on the road. I figure I spent enough money on the car, not to mention my house, that I'll spend a little more and get charging equipment installed to charge as safe as possible.
 

dtbaker61

Well-Known Member
First Name
Dan
Joined
May 11, 2020
Threads
126
Messages
4,822
Reaction score
4,524
Location
santa fe,nm
Website
www.envirokarma.org
Vehicles
MME (delivered 2/26/21), DIY eMiata BEV
Occupation
Solar Sales/install
Country flag
If you really want a safe applications, why use the NEMA outlet in the first place? Per the Munro Live episode, it is best to direct wire the to home EV equipment. I'm going to have the electrician do this when he installs my home equipment along with using THHN wire instead of Romex (higher temp rating and higher current rating). I would think this could end up saving you money on the install as well since you don't need the outlet nor the GFI breaker (although the wire is probably more expensive).
I prefer an outlet in my garage for a couple reasons:
- easy to get another charger if one dies
- easy to take with you if you sell the house
- outlet can be used for other 240v tools, like a welder
- outlet can be used in an emergency to backfeed Generator power to the whole house. (with proper procedure to isolate from Grid, and avoid exposure to live prongs with proper procedure)
 

Triggerhappy007

Well-Known Member
Joined
Feb 20, 2021
Threads
10
Messages
899
Reaction score
812
Location
TX
Vehicles
23 Premium, 3rd Mach-E
Country flag
I prefer an outlet in my garage for a couple reasons:
- easy to get another charger if one dies
- easy to take with you if you sell the house
- outlet can be used for other 240v tools, like a welder
- outlet can be used in an emergency to backfeed Generator power to the whole house. (with proper procedure to isolate from Grid, and avoid exposure to live prongs with proper procedure)
I prefer hardwired and plug in, so I have both. :)
 

shelnian

Well-Known Member
First Name
Ian
Joined
Apr 25, 2022
Threads
1
Messages
407
Reaction score
295
Location
Seattle
Vehicles
2022 MME Premium AWD, 2023 Lightning XLT SR 312A
Occupation
Retired
Country flag
Heat in electrical connections is caused by resistance between the contacts. This is what causes failures in the HVBJB as well. This heat is equal to the current squared times the resistance. This is why higher currents lead to more failures (like DC fast charging for the HVBJB). This means it's very important to reduce the contact resistance. Generally the more metal to metal contact area in a connection, the lower the resistance.

The reason why the Hubbell and Bryant outlets are superior is because the wire lug boxes use a heavy duty, large contact area, V shape that when tightened gathers the wire strands together, increasing contact area. The cheap outlets use smaller contact area, almost flat, contacts that tend to separate the wire stands so have a much reduced contact area compared to the Hubbell and Bryant outlets. The Hubbell and Bryant outlets also require a torque of 75 in. pounds instead of 25 like the cheap ones because of this larger contact surface area. They handle higher temperatures than the cheap outlets. They also have heavier one piece power and ground contacts that the EVSE plugs into. This increases plug-unplug cycle life. None of the cheap outlets can compare.

Cleanliness is important because corrosion, dirt, and carbon can greatly increase resistance. Making sure the EVSE plug contacts are clean and free from damage before plugging it into an outlet will increase outlet life and a chance of a melt down.

Outlet should be inspected and re-torqued periodically. If the outlet feels loose when plugging and unplugging or is damaged, it should be replaced immediately.
 

blkadr08

Well-Known Member
First Name
Bob
Joined
Jun 18, 2021
Threads
19
Messages
311
Reaction score
304
Location
Palm Desert
Vehicles
2021 MachE Premium XR
Occupation
Retired
Country flag
Very insightful video. I did not see a solid conclusion for reducing the fire hazard of charging at home? Did anyway else? I know he mentioned using the Hubble outlet and having a dedicated charger hardwired into the house but that was it.
I agree. Pretty good problem statement, no clear solution other than don’t buy a cheap dryer outlet. It did make me go out and check my install. Great post!
 
Last edited:

Vulnox

Well-Known Member
Joined
Nov 12, 2021
Threads
9
Messages
1,087
Reaction score
1,802
Location
Livonia, MI
Vehicles
2024 F-150 Lightning Platinum, 2025 Mach-E Premium AWD ER
Country flag
I agree. Pretty good problem statement, no clear solution other than don’t buy a cheap dryer outlet. It did make me go out and check my install. Great post!
Well I think it's because there is no such thing as a full solution. All you can do is give tips to reduce the chances. It's not like an EVSE install is the only source of electrical fire in the house. You can have an electrical fire from a standard 120 outlet with worn out pressure contacts and some dangling curtains. Or someone running an electric heater with worn out outlets and possibly undersized wiring in the walls because 30 years ago someone cut corners.

It's all about reducing risk, I can't imagine eliminating risk is even possible.

I am surprised there aren't thermal detection circuits in these outlets or on the EVSE plugs. With the C-Max Energi, they had a problem with melting/overheating plugs on the included 120 charger. Ford released a revised version in a recall after 2015 with a thermal sensor in the plug that would shut down the EVSE if it detected high temps at the plug. How that isn't standard on all EVSEs is the question I have.
 

Polar

Well-Known Member
First Name
SBJ
Joined
Jun 5, 2021
Threads
25
Messages
652
Reaction score
1,142
Location
PNW
Vehicles
2021 Select RWD SR
Country flag
Most all residential panels are press on. Most all commercial panels have bolt on breakers. Bolt down breakers are a much more positive method and superior to the press on type.
So for all of those at home with commercial panels… they’re set! ?