Thanks @65MustangBoy ! Appreciate your response. When I got my Mach E in Dec 2023, I used the Ford Mobile Charger with a 110V outlet as the 240V cable that came with it, would not fit my dryer plug. I then had a Ford Connected Charger installed professionally, and it is hardwired, and configured to provide 48A, and is connected to a 60A breaker. I know this, as when they first installed it, they used a 50A breaker, and I had to call them to correct it. This was Qmerit who arranged the installation FWIW. Thanks again!I'm an EE and don't usually jump into these topics. However, the answer to your question is sort of... yes. A NEMA 14-50 is RATED up to 50 amps at 240V. So you also need 50-amp capable wiring from the outlet to the 50-amp circuit breaker in your panel. I hope that makes sense. You should NOT connect a NEMA 14-50 to wiring that is only capable of handling 30 amps. And you certainly CANNOT just swap out a 30-amp breaker with a 50-amp breaker and leave your 30-amp cabling in-between. The wire will get HOT. To be clear the scenario I just described is a NEMA 14-50 with 30 amp wiring to a 50-amp breaker. (BIG NO-NO).
This is why there are different configurations of 240V outlets and plugs. Just because they are 240V capable, you CANNOT ignore the amp carrying capability all the way from the breaker panel, the breaker, the wiring, and the outlet. One of the primary benefits of 240 circuitry is the additional amp carrying capability it has.
My last point is the topic of "continuous use." To avoid a possible fire in the future I always design for worse case. That means I assume "continuous use" whether I use it continuously or not. For continuous use you want to only run at 80% of what the circuit is actually capable of. That being said... That means if you run a 60amp breaker, 60 amp carrying wiring, to a 60 amp termination. I used the word termination as this is the way many "hard wired" ESVE's are used. There is no outlet/plug. They are hardwired in. So for a 60 amp, hardwired ESVE I still would only ever run it at 48 amps (80% * 60 amps).
For your 50 amp NEMA 14-50 outlet/plug combination I would still limit the EVSE to 40 amps (80% x 50amps).
I hope this helps.