Just to confirm this is exactly how mine is set up: there is no special connection between the conduit and neutral bus.The conduit is connected to ground at the panel by virtue of the fitting screwed to the box itself (some special bonding may be required if the connector is installed in a concentric knockout). I don't see how, or why someone would go out of their way to try and make a connection between the conduit and the neutral bus.
I was just trying to say in my post that the conduit is bonded to neutral at the panel, but like you said just by virtue of being in contact.