Looks good, nice and clean! I do like hardwired installs, I think they make more sense for a long-term installation. In my case I hardwired my charger, but also installed a 2nd circuit with a NEMA 14-50R so I have a backup (or in the future, can charge two EVs).
For everyone wondering on the ampacity, yes, #6 is OK for a 70A breaker and a 50A continuous load (it works whether you rate the wire at 75C or 90C, and in both cases assume the terminals are only 75C).
My only suggestion would be that it would have been better to connect the green wire instead of the white wire since that terminal is for an equipment grounding conductor, not a neutral. You don't actually need the white wire at all (though it isn't hurting anything by being there).
In this case it is somewhat academic because as you say they go to the same place, but it is technically incorrect and could be caught by a future inspector. It probably wouldn't have any kind of actual practical impact unless you got a whole-house GFP in the future.
Just a suggestion, I would terminate the green on the line side to be consistent with the load side color coding. Then I would pull the white completely out of the circuit conduit as it’s unnecessary for the Home Flex. Not a good practice to leave an orphaned wire in a high amp box. Sometimes it’s necessary with Romex to wire nut and tape off an unused wire, but not if using individual THHN in conduit.
This is all very valuable feedback. Thanks for the information. I pulled 4 wires in the event I chose an EVSE that required a neutral and ground landing point.@connoisseurr this is going to get some critique.
Should have used #4 THHN if using a 70A breaker. #6 THHN is sized for 60A. Need to use the 75C column(see NFPA 70 110.14(C)(1)(a)) of NFPA 70 Table 310.15 (B)(16), assuming this run is directly from panel to charger (it should be as nothing else is permitted to be on an EV circuit). Not sure why pull the extra wire. I would terminate the green (ground) wire, not the white. If you want to land the white, it should be marked with green tape. The Chargepoint requires 2 hot (black & red) + 1 ground. If your panel has both ground and white on the same bar, I hope your panel is wired up correctly. This is only permitted if the neutral and ground are bonded IN the panel.
Did a nice job training the Flex. I would have used EMT straight down from the ceiling, then flex right into the bottom of the charger box. Could have used 3/4” conduit the whole way but its OK to up a trade size.
I did contemplate going #4 until my uncle (master electrician 30+ years), neighbor (commercial electrician 16 years), and a local reputable EVSE installer all identified #6 being acceptable and allowable for local building code.
My neutral bus and ground bar are bonded at the panel (new panel also installed early this year to support electric tankless and a few circuits for crypto mining). The white wire is indeed tagged at both ends indicating a grounded termination. Did that before commissioning the circuit.