Exactly, don't put something rated for only 50 amps with a breaker that trips at 60.A NEMA 14-50 outlet can only be connected to a 50 Amp breaker from everything I have read and understood here and other places. A 60 Amp breaker circuit is ONLY for hardwiring directly to the device without a plug. That being said, I assume you could remove the outlet of a 50 Amp circuit and hardwire the Ford Charger and it will work fine with the lower amperage. It just won't work at its highest output for charging - not that much of a difference if charging overnight.
If you want to start with a 50 amp breaker and 14-50 outlet, you could use 4 gauge wire and later "upgrade" by replacing the outlet with a hardwired charger and the 50 amp breaker with a 60 breaker.