From an engineering perspective, no. All a GFCI does is compare the current flowing in the conductors. If all is well, it should net to zero (same number of electrons going out as coming back, in simple terms). If the out vs in varies my more than 0.006 amperes, it trips. (UL states it must trip between 0.004 and 0.006).Are there any issues with plugging a device with it's own GFCI into a circuit with a GFCI breaker?
What can cause issues are surge protection schemes. Often surge protection circuitry connects from line to ground. If this circuit causes more than the 0.006 amps of leakage, the GFCI will trip. Devices that state not to connect to GFCI usually do so because of the type of internal surge protection they use.